Ive run my EMT conduit and placed my boxes in my workshop and placed the wires. All is good except... my inspector says I cant use conduit as ground and must run a bare or green conductor to each box/outlet... I dont want to get into rules/lawyering but what NEC line tells me (him) that conduit is OK for residential grounding. My city (Tucson) is on the 2017 NEC rev.
Am I reading this wrong?:
250.118 Types of Equipment Grounding Conductors. The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more or a combination of the following: (1) A copper, aluminum, or copper-clad aluminum conductor. This conductor shall be solid or stranded; insulated, covered, or bare; and in the form of a wire or a busbar of any shape. (2) Rigid metal conduit. (3) Intermediate metal conduit. (4) Electrical metallic tubing. ...
and this:
358.60 Grounding. EMT shall be permitted as an equipment grounding conductor.