1

I have a 220V 15 amp body dryer with 2 prongs on the plug (European). Manufacturer instructions indicate to connect 2 hots and 1 ground to the receptacle. Since this is in a bathroom, I have installed a GFCI 2 pole breaker, which requires a neutral from the receptacle. Without a neutral from the GFCI, the breaker trips. I just finished wiring my other GFCI single pole circuits to include the neutral from the receptacle, walla no more trips. How do I wire this? If I need to run a neutral, what size? I am using a 20 amp circuit.

3
  • Where are you on this planet? Commented Apr 23, 2019 at 1:23
  • I am located in California
    – user96567
    Commented Apr 23, 2019 at 3:51
  • 1
    What make and model is your panel, and the GFCI breaker in question? Also, it sounds weird that a GFCI would require a load-side neutral for a 220V only appliance... Commented Apr 23, 2019 at 11:42

1 Answer 1

2

GFCIs work by making sure current is equal in and out (i.e. that all current is accounted for). As such, all (normal) current must pass through a GFCI device: All hots and any neutral.

Normally one attaches the neutral wire to the neutral bar. The GFCI instructions are warning that you can't do the normal thing, and "the" neutral wire must go through the GFCI breaker (for detection purposes) just like all the hot(s).

Since your circuit does not employ a neutral wire, this advice is irrelevant to you.


When wiring this circuit, you may find it prudent to run a /3 cable so it can be used later for some other appliance which may want neutral. In that case, leave the full length on the neutral wires, but cap them off.


All that said, the GFCI breaker will have a "neutral pigtail" (literally looks like a pig's tail, it's all curled up) -- this is where the GFCI gets the supply-side neutral from. You will probably need to plug that into the neutral bar on the panel; many 240V GFCIs need it to power their own onboard electronics.

As with all GFCIs, hook up the GFCI itself and get it fully working before attaching anything to the load side. You will easily catch any such problem in this area.