How can I install a 40A 220V GFCI breaker in a main panel that has ground and neutral wires on the same bus bar?
I tried putting both white wires on the one bus bar that has the line feed neutral and a #1 copper wire and ground rod attached to it, but it keeps popping with no load.
-
1Did you connect the white wire from the branch circuit cable to the neutral bar, or to the breaker?– ThreePhaseEelCommented Oct 12, 2016 at 3:43
-
Hello, and welcome to Stack Exchange. This sounds like a job for a professional.– Daniel GriscomCommented Oct 12, 2016 at 11:03
-
I wouldn't say "professional" but I would say that you have not yet realized an essential fact of how GFCI devices function.– Harper - Reinstate MonicaCommented Oct 12, 2016 at 15:02
Add a comment
|
1 Answer
There should be no problem with this, as long as you've installed the breaker properly.
- Read and understand all of the included manufacturers documentation.
- Connect the grounded (neutral) pigtail from the breaker to the neutral/ground bar in the panel.
- Connect the grounded (neutral) circuit conductor to the neutral (silver) terminal on the GFCI breaker.
- Connect the ungrounded (hot) circuit conductors to the hot (brass) terminals on the GFCI breaker (one conductor per terminal).
If the breaker will not set, there are a few things that can be wrong.
- The breaker is faulty.
- There's a ground-fault in the circuit.
- There's a short-circuit in the circuit.
- The circuit is overloaded.
-
i did connect the neutral circuit conductor to the neutral / ground bar ! so i will reconnect it to the breaker and that should do it ! thanks I'll let you know how ti works out Commented Oct 12, 2016 at 12:34
-
so the ground wire from the circuit should still go to the neutral/ground bar right ? Commented Oct 12, 2016 at 12:38
-
@joecollier Yes, the grounding (earth) conductor goes to the neutral/ground bar. Commented Oct 12, 2016 at 14:10
-
success ! I feel like such a dummy ... Iv'e been retired for 12 years and just forgot how the wiring went. thanks Tester 101! you're help is greatly appreciated. I was a maintenance supervisor for 3 motels in Monterey Ca. for over 30 years and did most of the electrical work myself, once again ... thank you Commented Oct 12, 2016 at 22:34