I came across this APC product page for Microsol Isolator Modules, which purportedly provide "safe power in places with poor or nonexistent grounding." The unit is meant for Brazil, so it won't work in my case, but I'm wondering what the underlying technology or implementation is and if it provides some kind of "virtual ground" to simulate an actual ground.

I live in Argentina, where most houses are built out of concrete and many are old enough not to have ground wires running through the walls. I live in a second story apartment with no ground wires, no radiators or accessible cold water pipes. From what I can tell, running a ground wire through the wall would entail tearing down a significant portion of the walls and would be quite costly. The climate where I'm at is similar to Arizona, so I'm not even sure I could get to the water table if, in the unlikely event that the landlord and the downstairs neighbors were to give me permission to place a grounding rod in their interior garden below.

If I used a bootleg ground in combination with a GFCI outlet, would the GFCI kill the neutral end of the socket and prevent current from being pushed from neutral to "ground" to my equipment? Ground is tied to neutral at the service entrance but nowhere in the walls. Is there some other kind of second circuit breaker or box I could install in my room with a computer and ups that would be more like what's at the service entrance and less like a bootleg ground?

There is a metal gas pipe outside of my window. How dangerous would that be to use as a ground?

I have a door in my bedroom that the landlord has sealed off with duct tape because it opens to a staircase that leads down to the neighbor's garden. If I were to take the door out and seal it with concrete, sticking rebar in the wet cement, could I build an "Ufer" ground or does that have to be under actual ground?

Any better ideas than sticking a nail in the wall and calling it "ground?" This slightly absurd sounding "method" gives me a reading of 300 Ohms from neutral and a difference of about 15 volts when connected to hot (220 volts), compared to a hot-neutral reading (235 volts).

Electricity in Argentina is single phase, ~220v, 50Hz. We use a mix of older style European two prong cylindrical outlets and newer, three prong, Chinese/Australian style plugs (with neutral and hot reversed). Getting shocked by refrigerators when barefoot is almost a given here and almost everyone uses voltage regulators to deal with power irregularities. When testing outlets at home, I can see the voltage spiking to 1000 volts on my multimeter every few seconds, but only on some outlets (all are single-phase, 220v). What other kinds of voltage regulators will work without ground? Most of my electronics are dual voltage, so ideas including transformers that step down to 110-125v would be fine too.

Can I hook a voltage regulator up to a GFCI outlet and then hook a UPS into the voltage regulator to deal with nuisance trips from the GFCI and avoid hard drive failure? Can I still get surge protection without ground?

Other stupid grounding ideas: There's a grid of galvanized steel cables, spaced about one foot apart and set into the concrete walls outside which are there to hold up a grapevine. The cables are about the same gauge as a fence, maybe slighly thicker than the copper electrical wires in the wall. If I get good readings on the multimeter, can I use that as a ground? Will it electrocute the neighbor's cats who climb up on the vines or burn the grapevine? What would "good readings" (volts/ohms) be from the multimeter?

Box photos New yellow wire rust

9
  • My general sentiments about electricians and attitudes toward grounding are similar to those that I found on the following page about Thailand: thailandguru.com/grounding-earthing-electrical.html
    – Adam
    Commented Apr 26, 2015 at 21:56
  • Is the existing wiring not running in conduit? Surely the wires aren't set directly in the concrete? Can't you just fish an addition wire through the conduit for grounding? Commented Apr 26, 2015 at 23:06
  • I'm pretty sure there's a conduit in the wall, but there's no access panel to fish things through. Sometimes there are circular access panels above switches and sockets near the ceiling here that get capped off with small plastic discs, but I don't have that in my apartment. Moving seems like a good solution, but it's out of the question for the time being.
    – Adam
    Commented Apr 26, 2015 at 23:59
  • Can't you fish directly between the boxes in the wall? Commented Apr 27, 2015 at 0:19
  • @Adam -- are the boxes and conduits metal or plastic? Commented Apr 27, 2015 at 0:50

1 Answer 1

2

I came across this APC product page for Microsol Isolator Modules, which purportedly provide "safe power in places with poor or nonexistent grounding."

This is probably an isolating transformer, which ensures no current can flow to ground, even if you touch the live wires. The only way to get shocked is to touch both the output live and neutral. Requires a rather bulky, heavy, expensive transformer, though.

If I used a bootleg ground in combination with a GFCI outlet, would the GFCI kill the neutral end of the socket and prevent current from being pushed from neutral to "ground" to my equipment?

The main issue with this, I believe, is that neutral and live may be swapped somewhere - this would make your chassis live. There may also be a slight difference in the neutral voltage, due to voltage drop. As such, it's preferable to leave the ground floating, and trust the RCD/GFCI to trip if something goes wrong.

Ground is tied to neutral at the service entrance but nowhere in the walls. Is there some other kind of second circuit breaker or box I could install in my room with a computer and ups that would be more like what's at the service entrance and less like a bootleg ground?

It would be electrically the same as a bootleg ground, really. Unless you added another ground electrode.

When testing outlets at home, I can see the voltage spiking to 1000 volts on my multimeter every few seconds, but only on some outlets (all are single-phase, 220v). What other kinds of voltage regulators will work without ground? Most of my electronics are dual voltage, so ideas including transformers that step down to 110-125v would be fine too.

The best place to put a surge protector is in your main switchboard, because it covers everything and has the best ground. You should be able to get surge protectors specifically intended for here.

Can I hook a voltage regulator up to a GFCI outlet and then hook a UPS into the voltage regulator to deal with nuisance trips from the GFCI and avoid hard drive failure? Can I still get surge protection without ground?

I don't think the surge protectors are anywhere near as effective without a ground. You also need to make sure all the other cables going to your PC (especially coax internet) go through it.

There's a grid of galvanized steel cables, spaced about one foot apart and set into the concrete walls outside which are there to hold up a grapevine. The cables are about the same gauge as a fence, maybe slighly thicker than the copper electrical wires in the wall. If I get good readings on the multimeter, can I use that as a ground? Will it electrocute the neighbor's cats who climb up on the vines or burn the grapevine? What would "good readings" (volts/ohms) be from the multimeter?

If they're connected to the reinforcing bars in the concrete, this could be a good ground. Remember to tie the neutral to your grounding rod - without this bond, it's almost useless.

There isn't an easy way to test that it's a good ground.