1

I have an older 220V heater that came with the house I bought. It worked wonderfully for years, but then a wire burned out and each time I replace it, it burns out again within a week. The original wires were some kind of cloth-covered wire and there are still some of the original wiring, I have only replaced the burnt-out wires. One in particular keeps burning out. It connects to the screw which connects to the heater coils in the front. I have used all gauges of stranded wire and I have used solid wires. I use a ring terminal to connect the wire to the screw.

What can I do to fix this once and for all? Is there a certain type and gauge of wire to use? A different connector?

enter image description here enter image description here

4
  • Wires burn out for one of two reasons. One is they are too small. The size of the breaker will determine wire size. 10 gauge on 30 amps, 8 gauge for 40 amps, this is the minimum allowed, larger gauges are allowed. The second reason is poor connection, either loose/not tighten enough, or the connection is dirty/rusty.
    – crip659
    Commented Oct 8, 2023 at 10:59
  • 1
    For that? Take it to the scrapyard before it sets something on fire.
    – Ecnerwal
    Commented Oct 8, 2023 at 12:26
  • 4
    Look up 'sunk cost fallacy'. That death-trap is illegal these days.
    – Tetsujin
    Commented Oct 8, 2023 at 13:21
  • 1
    What is the temperature rating of the replacement wire? Commented Oct 8, 2023 at 19:26

1 Answer 1

1

A burnt wire in an appliance is very bad. This implies couple of things:

  • over-current fault causing the load to exceed initial specification
  • connection have corroded and can no longer handle the load

Neither are trivial. Both are turning said wire into a heating element, which is causing it to "burn out".

Fixing this is non-trivial. For the first one, it is a write-off. There's no point of even trying, and you risk making it worse.

For the second point, you'll have to spend time cleaning up the connection. Most of the time, the appliance is usually made in such a way that doing this is extremely impractical. I've fixed my kettle that had a corroded contact so YMMV, but it involves taking the whole thing apart, getting sandpaper in there, and sanding the thing down, then making a really good connection so the problem doesn't repeat.

2
  • Thank you for responding. I have now taken out the heater and installed a plug instead in preparation for another heater (the old one was wired directly). However, when testing the plug, I noticed that the lamp that I plugged into it is much brighter than when I plug it into a different plug. Is this an over-current fault? What causes that?
    – zynovij
    Commented Oct 23, 2023 at 23:07
  • @AlexaKirk That's a completely separate question.
    – Nelson
    Commented Oct 25, 2023 at 1:36

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.