It’s a 3 way closet switch, when I flip it up to turn on the closet light on it turns off the kitchen light. The kitchen receptacles are cut off from power and also the kitchen fan aso gets cut off. When I flip the closet light switch down to turn off closet light the kitchen light turns on etc... The hot wire is connected to the black nut.
1 Answer
Based on a hunch from the comments, I think this is a 3-way switch that replaced a regular switch, and that the reason it is a 3-way switch is not because a 3-way switch is actually needed, but rather because the original switch had two black wires, one on a screw and the other as a backstab connection, and whoever replaced the switch assumed that the three wires (two black, one red) were from a 3-way switch and not "two wires combined together and a third wire separate".
Assuming that's the case, the two black wires should be connected together, just as the screw and backstab are internally connected together. Two ways to do that:
- Add a short piece of 12 AWG black wire (a.k.a. pigtail). Use a wire nut to connect it to the two black wires from the switch and connect it to the black screw on the switch (assuming that there is one black screw and two brass screws - if it is one brass screw and two black screws then connect it to the brass screw). Note that there is absolutely nothing wrong with using a 3-way switch this way as a regular switch. If after doing this you find that the switch seems "upside down", just turn it around or move the red wire to the other (now unused) screw.
- Swap for a high quality regular switch, such as this Leviton switch:
The key is a feature called "screw to clamp", though some manufacturers have a fancy name for it. What that lets you do is slide a straight wire under each side (top and bottom) of each screw by putting it under a clamp that is tightened when you tighten the screw. That saves the time and trouble of making the wire into a hook and it allows you to have two wires on a single screw. The picture is not 100% clear, but it looks like the existing switch may have screw to Clamp. Trim each of the black wires 1/4" and straighten and slide under the clamp, one below the screw, one above, and tighten the screw.
-
I agree with everything you said. But OP stated that the closet light and the kitchen stuff are far away from each other. If that's case, it does not make sense, at least in my mind, that the original switch was controlling both locations.– SteveShCommented Aug 1, 2022 at 0:19
-
1That's the point. The switch wasn't controlling the kitchen. But the hot wire used the switch as a junction. Commented Aug 1, 2022 at 0:26
-
2Okay I did what /manassehkatz-moving-2-codidact told me to do and it had been resolved. I bought a single pole switch, connected the red traveler to the top terminal, connected both hot and black traveler to the bottom terminal, connected the ground to ground terminal and walaaa!! It has been fixed. Thanks a bunch. Commented Aug 1, 2022 at 6:55
-
1Now, @JoseLeon — mark this answer as accepted. Congrats on fixing this. Commented Aug 1, 2022 at 12:52
-