Is the following installation method for NM cable clamps prohibited by the NEC for receptacle outlets?

##Is the following installation method for NM cable clamps prohibited by the NEC for receptacle outlets? ## Note: I know it would be more functional and less awkward to screw in the NM clamps had I used one of the knockouts on top of the box (indicated by the green arrow), right side, or bottom of the box. However, this was the only box I had laying around that already had a knockout punched out for an example and I was able to use a right angle driver to secure the NM clamps for this example setup. Also, since I know I will receive comments if I don't clarify: I know the metal box needs to be grounded (e.g. green ground screw and pigtail) even though it is not shown in the pictures below.

NM cable clamp screws inside box -- seen from outside box NM cable clamp screws inside box -- seen from outside box

This is what I have typically seen for instructions on installing NM cable clamps:

NM cable clamp screws outside box -- seen from outside box NM cable clamp screws outside box -- seen from outside box**

Reason for Question:

While I know the "reversed" method of installing cable clamps will take up additional space inside the box, if I use a 4"x4"x2+" box for a single gang outlet (using a single gang mud ring) then crowding the box is definitely not an issue. Also, if I leave a few inches of slack in the cable outside of the box, I can loosen the clamp to give me some "wiggle room" if I (or a future owner) is doing some work and needs extend the cable a little for any reason without having to tear open the drywall around the box or splice in pigtails.

##Is the following installation method for NM cable clamps prohibited by the NEC for receptacle outlets? ## Note: I know it would be more functional and less awkward to screw in the NM clamps had I used one of the knockouts on top of the box (indicated by the green arrow), right side, or bottom of the box. However, this was the only box I had laying around that already had a knockout punched out for an example and I was able to use a right angle driver to secure the NM clamps for this example setup. Also, since I know I will receive comments if I don't clarify: I know the metal box needs to be grounded (e.g. green ground screw and pigtail) even though it is not shown in the pictures below.

NM cable clamp screws inside box -- seen from outside box NM cable clamp screws inside box -- seen from outside box

This is what I have typically seen for instructions on installing NM cable clamps:

NM cable clamp screws outside box -- seen from outside box NM cable clamp screws outside box -- seen from outside box**

Reason for Question:

While I know the "reversed" method of installing cable clamps will take up additional space inside the box, if I use a 4"x4"x2+" box for a single gang outlet (using a single gang mud ring) then crowding the box is definitely not an issue. Also, if I leave a few inches of slack in the cable outside of the box, I can loosen the clamp to give me some "wiggle room" if I (or a future owner) is doing some work and needs extend the cable a little for any reason without having to tear open the drywall around the box or splice in pigtails.

Is the following installation method for NM cable clamps prohibited by the NEC for receptacle outlets?

Note: I know it would be more functional and less awkward to screw in the NM clamps had I used one of the knockouts on top of the box (indicated by the green arrow), right side, or bottom of the box. However, this was the only box I had laying around that already had a knockout punched out for an example and I was able to use a right angle driver to secure the NM clamps for this example setup. Also, since I know I will receive comments if I don't clarify: I know the metal box needs to be grounded (e.g. green ground screw and pigtail) even though it is not shown in the pictures below.

NM cable clamp screws inside box -- seen from outside box NM cable clamp screws inside box -- seen from outside box

This is what I have typically seen for instructions on installing NM cable clamps:

NM cable clamp screws outside box -- seen from outside box NM cable clamp screws outside box -- seen from outside box**

Reason for Question:

While I know the "reversed" method of installing cable clamps will take up additional space inside the box, if I use a 4"x4"x2+" box for a single gang outlet (using a single gang mud ring) then crowding the box is definitely not an issue. Also, if I leave a few inches of slack in the cable outside of the box, I can loosen the clamp to give me some "wiggle room" if I (or a future owner) is doing some work and needs extend the cable a little for any reason without having to tear open the drywall around the box or splice in pigtails.

Tweeted twitter.com/StackDIY/status/741469628610818048
added 20 characters in body
Source Link
statueuphemism
  • 5.3k
  • 13
  • 50
  • 65

##Is the following installation method for NM cable clamps prohibited by the NEC for receptacle outlets? ## Note: I know it would be more functional and less awkward to screw in the NM clamps had I used one of the knockouts on top of the box (indicated by the green arrow), right side, or bottom of the box. However, this was the only box I had laying around that already had a knockout punched out for an example and I was able to use a right angle driver to secure the NM clamps for this example setup. Also, since I know I will receive comments if I don't clarify: I know the metal box needs to be grounded (e.g. green ground screw and pigtail) even though it is not shown in the pictures below.

NM cable clamp screws inside box -- seen from outside box NM cable clamp screws inside box -- seen from outside box

This is what I have typically seen for instructions on installing NM cable clamps:

NM cable clamp screws outside box -- seen from outside box NM cable clamp screws outside box -- seen from outside box**

Reason for Question:

While I know the "reversed" method of installing cable clamps will take up additional space inside the box, if I use a 4"x4"x2+" box for a single gang outlet (using a single gang mud ring) then crowding the box is definitely not an issue. Also, if I leave a few inches of slack in the cable outside of the box, I can loosen the clamp to give me some "wiggle room" if I (or a future owner) is doing some work and needs extend the cable a little for any reason without having to tear open the drywall around the box or splice in pigtails.

##Is the following installation method for NM cable clamps prohibited by the NEC for receptacle outlets? ## Note: I know it would be less awkward to screw in the NM clamps had I used one of the knockouts on top of the box (indicated by the green arrow), right side, or bottom of the box. However, this was the only box I had laying around that already had a knockout punched out for an example and I was able to use a right angle driver to secure the NM clamps for this example setup. Also, since I know I will receive comments if I don't clarify: I know the metal box needs to be grounded (e.g. green ground screw and pigtail) even though it is not shown in the pictures below.

NM cable clamp screws inside box -- seen from outside box NM cable clamp screws inside box -- seen from outside box

This is what I have typically seen for instructions on installing NM cable clamps:

NM cable clamp screws outside box -- seen from outside box NM cable clamp screws outside box -- seen from outside box**

Reason for Question:

While I know the "reversed" method of installing cable clamps will take up additional space inside the box, if I use a 4"x4"x2+" box for a single gang outlet (using a single gang mud ring) then crowding the box is definitely not an issue. Also, if I leave a few inches of slack in the cable outside of the box, I can loosen the clamp to give me some "wiggle room" if I (or a future owner) is doing some work and needs extend the cable a little for any reason without having to tear open the drywall around the box or splice in pigtails.

##Is the following installation method for NM cable clamps prohibited by the NEC for receptacle outlets? ## Note: I know it would be more functional and less awkward to screw in the NM clamps had I used one of the knockouts on top of the box (indicated by the green arrow), right side, or bottom of the box. However, this was the only box I had laying around that already had a knockout punched out for an example and I was able to use a right angle driver to secure the NM clamps for this example setup. Also, since I know I will receive comments if I don't clarify: I know the metal box needs to be grounded (e.g. green ground screw and pigtail) even though it is not shown in the pictures below.

NM cable clamp screws inside box -- seen from outside box NM cable clamp screws inside box -- seen from outside box

This is what I have typically seen for instructions on installing NM cable clamps:

NM cable clamp screws outside box -- seen from outside box NM cable clamp screws outside box -- seen from outside box**

Reason for Question:

While I know the "reversed" method of installing cable clamps will take up additional space inside the box, if I use a 4"x4"x2+" box for a single gang outlet (using a single gang mud ring) then crowding the box is definitely not an issue. Also, if I leave a few inches of slack in the cable outside of the box, I can loosen the clamp to give me some "wiggle room" if I (or a future owner) is doing some work and needs extend the cable a little for any reason without having to tear open the drywall around the box or splice in pigtails.

Source Link
statueuphemism
  • 5.3k
  • 13
  • 50
  • 65

Is it against NEC to reverse NM cable clamps?

##Is the following installation method for NM cable clamps prohibited by the NEC for receptacle outlets? ## Note: I know it would be less awkward to screw in the NM clamps had I used one of the knockouts on top of the box (indicated by the green arrow), right side, or bottom of the box. However, this was the only box I had laying around that already had a knockout punched out for an example and I was able to use a right angle driver to secure the NM clamps for this example setup. Also, since I know I will receive comments if I don't clarify: I know the metal box needs to be grounded (e.g. green ground screw and pigtail) even though it is not shown in the pictures below.

NM cable clamp screws inside box -- seen from outside box NM cable clamp screws inside box -- seen from outside box

This is what I have typically seen for instructions on installing NM cable clamps:

NM cable clamp screws outside box -- seen from outside box NM cable clamp screws outside box -- seen from outside box**

Reason for Question:

While I know the "reversed" method of installing cable clamps will take up additional space inside the box, if I use a 4"x4"x2+" box for a single gang outlet (using a single gang mud ring) then crowding the box is definitely not an issue. Also, if I leave a few inches of slack in the cable outside of the box, I can loosen the clamp to give me some "wiggle room" if I (or a future owner) is doing some work and needs extend the cable a little for any reason without having to tear open the drywall around the box or splice in pigtails.