Feb 1, 2016 at 15:55 history edited ArchonOSX CC BY-SA 3.0
removed instantaneous for accuracy
Feb 1, 2016 at 13:39 comment added Tester101 I've added what I feel is a fairly accurate example to my answer.
Feb 1, 2016 at 10:45 comment added ArchonOSX True, but that wire is going to be considerably larger and have much less resistance. 200' of #4 has .05 ohms of resistance. Considering that. If the fault were to occur in the feeder or closer to the sub-panel the fault current would be considerably higher.
Jan 31, 2016 at 23:48 comment added Tester101 a 50' circuit would only be 25' away from the panel (along the wire). You also have to consider the circuit from the main panel to the second panel, and back.
Jan 31, 2016 at 23:29 comment added ArchonOSX Yes, but that is at 200 feet of #14 that would be at the extreme of most dwelling units. The average would usually be closer to the 50 feet so almost 1000 amps or even more if it was #12 wire. Certainly the magnetic trip will come in well before the thermal trip at these levels. It would be nice if the smallest breaker trips first but I wouldn't bet a paycheck on it.
Jan 31, 2016 at 22:23 comment added Tester101 238 amperes is only 1.19 times the rated current of a 200 ampere breaker, and 2.38 times the 100 ampere breakers. That's likely far below the instantaneous trip rating.
Jan 31, 2016 at 18:03 history answered ArchonOSX CC BY-SA 3.0