Short answer: No you don't need a ground wire. The code lets you replace the two wire receptacle with a GFCI.

From the 2011 National Electrical Code

406.4(D)(2)(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.

Happy Sunday!

Short answer: No you don't need a ground wire. The code lets you replace the two wire receptacle with a GFCI.

From the 2011 National Electrical Code

406.4(D)(2)(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.

Happy Sunday!

Short answer: No you don't need a ground wire. The code lets you replace the two wire receptacle with a GFCI.

From the 2011 National Electrical Code

406.4(D)(2)(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.

Source Link
ArchonOSX
  • 20.6k
  • 3
  • 29
  • 52

Short answer: No you don't need a ground wire. The code lets you replace the two wire receptacle with a GFCI.

From the 2011 National Electrical Code

406.4(D)(2)(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.

Happy Sunday!