Sep 24, 2015 at 1:06 | comment | added | Speedy Petey | OH!! Ok, sorry, I was looking at it backwards. That panel is in the RV, that is not the source panel. I thought you were wiring an RV receptacle. Either way, what you propose is fine. And yes, since it is a ML panel with more than 6 spaces you do need some form of service disconnect. | |
Sep 24, 2015 at 0:05 | vote | accept | Jimmy | ||
Sep 23, 2015 at 23:56 | comment | added | Jimmy | I have the disconnect as my 'Main Shutoff '. The feed is coming from a 50 Amp Receptacle Like this one homedepot.com/catalog/productImages/1000/84/… Im using 6 Gauge to wire it, was having concerns about the neutral since I need 240 and 120 | |
Sep 23, 2015 at 23:47 | comment | added | Tester101 | Also, I believe nothing is currently feeding the panel, since the feed will come from the disconnect. | |
Sep 23, 2015 at 23:46 | comment | added | Tester101 | The disconnect is required, because it looks like there's 8 handles in the panel. | |
Sep 23, 2015 at 23:38 | history | answered | Speedy Petey | CC BY-SA 3.0 |