Skip to main content
edited title
Link
Tester101
  • 132.5k
  • 79
  • 324
  • 612

Open Ground on Grounded Outlet Are grounded receptacles with open grounds causing my electrical problems?

edited body
Source Link

I have a room that has six outlets. Two of which are healthy with ground and ~120V coming through. The other four report open ground with one of the four not working at all (no juice). I've checked the voltage and the ground receptacles in the four don't respond at all (as in testing it with the Hot receptacle).

All outlets had ground at one point with two lost from a power outage a while back. The two I lost recently were from a safety practice that required me to power down the surge protectors, cutting power to the electronics connected to them.

Upon repowering them, the lights went out, but the breaker did not trip. A voltage test (eep!) at the breaker showed that the breaker (15A) was fine (pumping ~120v through). I should note that the outlets have two surge protectors connected with a variety of electronic devices connected including a PC, surround sound and a Dyson heater.

My current problem is that resetting the breaker doedid not restore power back to that room, and my only suspicion that its from the open ground outlets, but turning on more than one light outside the room can "trip" the circuit. What do I do?

I have a room that has six outlets. Two of which are healthy with ground and ~120V coming through. The other four report open ground with one of the four not working at all (no juice). I've checked the voltage and the ground receptacles in the four don't respond at all (as in testing it with the Hot receptacle).

All outlets had ground at one point with two lost from a power outage a while back. The two I lost recently were from a safety practice that required me to power down the surge protectors, cutting power to the electronics connected to them.

Upon repowering them, the lights went out, but the breaker did not trip. A voltage test (eep!) at the breaker showed that the breaker (15A) was fine (pumping ~120v through). I should note that the outlets have two surge protectors connected with a variety of electronic devices connected including a PC, surround sound and a Dyson heater.

My current problem is that resetting the breaker doe not restore power back to that room, and my only suspicion that its from the open ground outlets, but turning on more than one light outside the room can "trip" the circuit. What do I do?

I have a room that has six outlets. Two of which are healthy with ground and ~120V coming through. The other four report open ground with one of the four not working at all (no juice). I've checked the voltage and the ground receptacles in the four don't respond at all (as in testing it with the Hot receptacle).

All outlets had ground at one point with two lost from a power outage a while back. The two I lost recently were from a safety practice that required me to power down the surge protectors, cutting power to the electronics connected to them.

Upon repowering them, the lights went out, but the breaker did not trip. A voltage test (eep!) at the breaker showed that the breaker (15A) was fine (pumping ~120v through). I should note that the outlets have two surge protectors connected with a variety of electronic devices connected including a PC, surround sound and a Dyson heater.

My current problem is that resetting the breaker did not restore power back to that room, and my only suspicion that its from the open ground outlets, but turning on more than one light outside the room can "trip" the circuit. What do I do?

Source Link

Open Ground on Grounded Outlet

I have a room that has six outlets. Two of which are healthy with ground and ~120V coming through. The other four report open ground with one of the four not working at all (no juice). I've checked the voltage and the ground receptacles in the four don't respond at all (as in testing it with the Hot receptacle).

All outlets had ground at one point with two lost from a power outage a while back. The two I lost recently were from a safety practice that required me to power down the surge protectors, cutting power to the electronics connected to them.

Upon repowering them, the lights went out, but the breaker did not trip. A voltage test (eep!) at the breaker showed that the breaker (15A) was fine (pumping ~120v through). I should note that the outlets have two surge protectors connected with a variety of electronic devices connected including a PC, surround sound and a Dyson heater.

My current problem is that resetting the breaker doe not restore power back to that room, and my only suspicion that its from the open ground outlets, but turning on more than one light outside the room can "trip" the circuit. What do I do?