I had someone connect some romex for some wall lights for me. I ran the wire, and just had him do the connections (they're inside junction boxes). This from a partially finished space into a finished space. As the run starts it is in holes drilled through exposed 2x4 wall (the other side has drywall), it leaves the wall and goes out and over the metal support beam and into a finished drywall ceiling. It's stapled on the vertical part. On this part I use a flexible metal raceway (secured at both ends) to go over the beam (the builder did the exact same thing). After this, I ran the wire between the floor joists. I laid it on top of the ceiling that's finished with drywall.

I sold my house... it will be inspected...like.. in a couple days... do I need to tear out portions of the ceiling and staple this wire to the joists? Do I need to take it all out and have it pass, then have someone else come in and redo it? Will he get on a ladder and look at how it's run? Does it matter? Is it within code? Help me get this thing right so I can make sure our home closes. Thank you! (the wiring is part of a home theater that is being sold with the house.. it's a major player as to why our house is selling.. need to make sure there's not a surprise). Thanks

Btw, saw someone say on this site that it was ok to let it lay up there, and ran with it. Wish I wouldn't have done that now, just so that I wasn't worrying right now.

Edit from OP: Let me go further... Based on my limited knowledge, I understand that home inspectors (those generally hired by the buyer) are not "code experts". That said, my township requires an occupancy permit and inspection (ie, the city's building inspector comes out, I'm sure you know that :P). So, this guy might be a little more stringent when he finds work done that wasn't permitted. I'm not even sure it has to be permitted, but maybe it does? I'll be calling this week to find out and apply for retroactive if so. So, if it is required, it will be required to be up to code... Will the city's inspector pass it done this way? Here's a picture to illustrate. There are three of these coming from one closed junction box ran off an existing outlet ran parallel with the joists.

http://postimg.org/image/eql9ro465/enter image description here

I had someone connect some romex for some wall lights for me. I ran the wire, and just had him do the connections (they're inside junction boxes). This from a partially finished space into a finished space. As the run starts it is in holes drilled through exposed 2x4 wall (the other side has drywall), it leaves the wall and goes out and over the metal support beam and into a finished drywall ceiling. It's stapled on the vertical part. On this part I use a flexible metal raceway (secured at both ends) to go over the beam (the builder did the exact same thing). After this, I ran the wire between the floor joists. I laid it on top of the ceiling that's finished with drywall.

I sold my house... it will be inspected...like.. in a couple days... do I need to tear out portions of the ceiling and staple this wire to the joists? Do I need to take it all out and have it pass, then have someone else come in and redo it? Will he get on a ladder and look at how it's run? Does it matter? Is it within code? Help me get this thing right so I can make sure our home closes. Thank you! (the wiring is part of a home theater that is being sold with the house.. it's a major player as to why our house is selling.. need to make sure there's not a surprise). Thanks

Btw, saw someone say on this site that it was ok to let it lay up there, and ran with it. Wish I wouldn't have done that now, just so that I wasn't worrying right now.

Edit from OP: Let me go further... Based on my limited knowledge, I understand that home inspectors (those generally hired by the buyer) are not "code experts". That said, my township requires an occupancy permit and inspection (ie, the city's building inspector comes out, I'm sure you know that :P). So, this guy might be a little more stringent when he finds work done that wasn't permitted. I'm not even sure it has to be permitted, but maybe it does? I'll be calling this week to find out and apply for retroactive if so. So, if it is required, it will be required to be up to code... Will the city's inspector pass it done this way? Here's a picture to illustrate. There are three of these coming from one closed junction box ran off an existing outlet ran parallel with the joists.

http://postimg.org/image/eql9ro465/

I had someone connect some romex for some wall lights for me. I ran the wire, and just had him do the connections (they're inside junction boxes). This from a partially finished space into a finished space. As the run starts it is in holes drilled through exposed 2x4 wall (the other side has drywall), it leaves the wall and goes out and over the metal support beam and into a finished drywall ceiling. It's stapled on the vertical part. On this part I use a flexible metal raceway (secured at both ends) to go over the beam (the builder did the exact same thing). After this, I ran the wire between the floor joists. I laid it on top of the ceiling that's finished with drywall.

I sold my house... it will be inspected...like.. in a couple days... do I need to tear out portions of the ceiling and staple this wire to the joists? Do I need to take it all out and have it pass, then have someone else come in and redo it? Will he get on a ladder and look at how it's run? Does it matter? Is it within code? Help me get this thing right so I can make sure our home closes. Thank you! (the wiring is part of a home theater that is being sold with the house.. it's a major player as to why our house is selling.. need to make sure there's not a surprise). Thanks

Btw, saw someone say on this site that it was ok to let it lay up there, and ran with it. Wish I wouldn't have done that now, just so that I wasn't worrying right now.

Edit from OP: Let me go further... Based on my limited knowledge, I understand that home inspectors (those generally hired by the buyer) are not "code experts". That said, my township requires an occupancy permit and inspection (ie, the city's building inspector comes out, I'm sure you know that :P). So, this guy might be a little more stringent when he finds work done that wasn't permitted. I'm not even sure it has to be permitted, but maybe it does? I'll be calling this week to find out and apply for retroactive if so. So, if it is required, it will be required to be up to code... Will the city's inspector pass it done this way? Here's a picture to illustrate. There are three of these coming from one closed junction box ran off an existing outlet ran parallel with the joists.

enter image description here

updating question with "answer"
Source Link
BMitch
  • 43.1k
  • 15
  • 96
  • 202

I had someone connect some romex for some wall lights for me. I ran the wire, and just had him do the connections (they're inside junction boxes). This from a partially finished space into a finished space. As the run starts it is in holes drilled through exposed 2x4 wall (the other side has drywall), it leaves the wall and goes out and over the metal support beam and into a finished drywall ceiling. It's stapled on the vertical part. On this part I use a flexible metal raceway (secured at both ends) to go over the beam (the builder did the exact same thing). After this, I ran the wire between the floor joists. I laid it on top of the ceiling that's finished with drywall.

I sold my house... it will be inspected...like.. in a couple days... do I need to tear out portions of the ceiling and staple this wire to the joists? Do I need to take it all out and have it pass, then have someone else come in and redo it? Will he get on a ladder and look at how it's run? Does it matter? Is it within code? Help me get this thing right so I can make sure our home closes. Thank you! (the wiring is part of a home theater that is being sold with the house.. it's a major player as to why our house is selling.. need to make sure there's not a surprise). Thanks

Btw, saw someone say on this site that it was ok to let it lay up there, and ran with it. Wish I wouldn't have done that now, just so that I wasn't worrying right now.

Edit from OP: Let me go further... Based on my limited knowledge, I understand that home inspectors (those generally hired by the buyer) are not "code experts". That said, my township requires an occupancy permit and inspection (ie, the city's building inspector comes out, I'm sure you know that :P). So, this guy might be a little more stringent when he finds work done that wasn't permitted. I'm not even sure it has to be permitted, but maybe it does? I'll be calling this week to find out and apply for retroactive if so. So, if it is required, it will be required to be up to code... Will the city's inspector pass it done this way? Here's a picture to illustrate. There are three of these coming from one closed junction box ran off an existing outlet ran parallel with the joists.

http://postimg.org/image/eql9ro465/

I had someone connect some romex for some wall lights for me. I ran the wire, and just had him do the connections (they're inside junction boxes). This from a partially finished space into a finished space. As the run starts it is in holes drilled through exposed 2x4 wall (the other side has drywall), it leaves the wall and goes out and over the metal support beam and into a finished drywall ceiling. It's stapled on the vertical part. On this part I use a flexible metal raceway (secured at both ends) to go over the beam (the builder did the exact same thing). After this, I ran the wire between the floor joists. I laid it on top of the ceiling that's finished with drywall.

I sold my house... it will be inspected...like.. in a couple days... do I need to tear out portions of the ceiling and staple this wire to the joists? Do I need to take it all out and have it pass, then have someone else come in and redo it? Will he get on a ladder and look at how it's run? Does it matter? Is it within code? Help me get this thing right so I can make sure our home closes. Thank you! (the wiring is part of a home theater that is being sold with the house.. it's a major player as to why our house is selling.. need to make sure there's not a surprise). Thanks

Btw, saw someone say on this site that it was ok to let it lay up there, and ran with it. Wish I wouldn't have done that now, just so that I wasn't worrying right now.

I had someone connect some romex for some wall lights for me. I ran the wire, and just had him do the connections (they're inside junction boxes). This from a partially finished space into a finished space. As the run starts it is in holes drilled through exposed 2x4 wall (the other side has drywall), it leaves the wall and goes out and over the metal support beam and into a finished drywall ceiling. It's stapled on the vertical part. On this part I use a flexible metal raceway (secured at both ends) to go over the beam (the builder did the exact same thing). After this, I ran the wire between the floor joists. I laid it on top of the ceiling that's finished with drywall.

I sold my house... it will be inspected...like.. in a couple days... do I need to tear out portions of the ceiling and staple this wire to the joists? Do I need to take it all out and have it pass, then have someone else come in and redo it? Will he get on a ladder and look at how it's run? Does it matter? Is it within code? Help me get this thing right so I can make sure our home closes. Thank you! (the wiring is part of a home theater that is being sold with the house.. it's a major player as to why our house is selling.. need to make sure there's not a surprise). Thanks

Btw, saw someone say on this site that it was ok to let it lay up there, and ran with it. Wish I wouldn't have done that now, just so that I wasn't worrying right now.

Edit from OP: Let me go further... Based on my limited knowledge, I understand that home inspectors (those generally hired by the buyer) are not "code experts". That said, my township requires an occupancy permit and inspection (ie, the city's building inspector comes out, I'm sure you know that :P). So, this guy might be a little more stringent when he finds work done that wasn't permitted. I'm not even sure it has to be permitted, but maybe it does? I'll be calling this week to find out and apply for retroactive if so. So, if it is required, it will be required to be up to code... Will the city's inspector pass it done this way? Here's a picture to illustrate. There are three of these coming from one closed junction box ran off an existing outlet ran parallel with the joists.

http://postimg.org/image/eql9ro465/

Source Link

wiring for wall sconces

I had someone connect some romex for some wall lights for me. I ran the wire, and just had him do the connections (they're inside junction boxes). This from a partially finished space into a finished space. As the run starts it is in holes drilled through exposed 2x4 wall (the other side has drywall), it leaves the wall and goes out and over the metal support beam and into a finished drywall ceiling. It's stapled on the vertical part. On this part I use a flexible metal raceway (secured at both ends) to go over the beam (the builder did the exact same thing). After this, I ran the wire between the floor joists. I laid it on top of the ceiling that's finished with drywall.

I sold my house... it will be inspected...like.. in a couple days... do I need to tear out portions of the ceiling and staple this wire to the joists? Do I need to take it all out and have it pass, then have someone else come in and redo it? Will he get on a ladder and look at how it's run? Does it matter? Is it within code? Help me get this thing right so I can make sure our home closes. Thank you! (the wiring is part of a home theater that is being sold with the house.. it's a major player as to why our house is selling.. need to make sure there's not a surprise). Thanks

Btw, saw someone say on this site that it was ok to let it lay up there, and ran with it. Wish I wouldn't have done that now, just so that I wasn't worrying right now.