Sep 14 at 17:26 | comment | added | Fresh Codemonger | @RetiredMasterElectrician - When I change the pullout disconnect for a 50AMP GFCI breaker spakit CHOME250SPA does that change the voltage drop? Is the length the 53' tub to disconnect plus the 55' disconnect to panel for 108' ? The 53' is the 6/3 and the 55' is the 8/3. Canada. | |
Sep 12 at 5:39 | comment | added | Harper - Reinstate Monica | Teck is a Canadian invention (by the hard rock mining industry). NEC sees it as an enhanced MC cable with additional ratings by UL. This is authorized by NEC at 330.10(A)(6) and (12)... and 330.12(2). | |
Sep 10 at 12:40 | comment | added | Retired Master Electrician | @FreshCodemonger - Your length is going to get you about a 3% voltage drop from the panel to the tub which is right on the edge of acceptable for motors. Also if you are using the entire 43 Amps as a start up adding 25% will get you to 53.75 Amps. That means you are stressing your 50 Amp breaker at startup. Are you running this in Canada or the US? Is there a maximum circuit breaker size on the name plate? I still recommend you check with your AHJ. | |
Sep 9 at 22:25 | comment | added | ThreePhaseEel | TECK is basically a MC cable construction, and some but not all TECK cable is MC/TECK dual-rated (Belden's TECK cables are dual-rated, for instance, but not all are) | |
Sep 9 at 22:23 | comment | added | Fresh Codemonger | Name plate rating for the hot tub says 43 amps / 230 volts / 60 hz. Hot tub is 53` of teck cable from hot tub to disconnect. Disconnect to panel is probably about the same maybe 55`. | |
Sep 9 at 22:20 | comment | added | Fresh Codemonger | In Canada, teck cable is defined by CSA standard C22.2 No. 131[2] and carries the type designation of TECK90, the 90 referring to the maximum conductor temperature in degrees Celsius that the cable may be used at in a maximum 30 C ambient environment without de-rating its ampacity. en.wikipedia.org/wiki/Teck_cable | |
Sep 9 at 22:18 | comment | added | Fresh Codemonger | Does this help? northerncables.com/products/teck90 | |
Sep 9 at 22:09 | history | answered | Retired Master Electrician | CC BY-SA 4.0 |