I live in BC, so this is about 120VAC house wiring. I have an island in the kitchen that has two outlets on it. It used to have an electric cooktop (before I installed a gas cooktop) and that 30amp circuit is now just used for running the illumination for the gas top. The two outlets are on another circuit and wired strangely; one just simply chains off the other so let's ignore that. The supply line is a 14/3 with the red capped and not energized (checked with Klein tester).

When I put in my ET310 transmitter and check the service panel I find the Klein beeps when I hover over a double-pole 15 amp breaker (which has only ONE lever). This breaker is OFF all the time and when I attempt to turn it ON, it shorts out, there's a spark in the panel (!) and the breaker immediately opens. This was the situation when we bought the house and as it never seemed to affect anything I just left it off, thinking someday I'll get to it...

So, the primary outlet in the island started to act erratically, shutting off and on for no reason so I decided to investigate and this is how I found that the Klein traces the circuit to this double-pole breaker. Now, I'm thinking that the guy wired this circuit incorrectly and effectively somehow looped the two phases on the 14/3. I haven't yet opened up the panel (this is difficult for stupid reasons) to see what's up but was hoping someone had an idea of what's going on here?


Thanks guys but I guess I wasn't as clear as I thought I was being. Forget the 30A circuit used for the few watts the cooktop illumination uses; I understand that 30A is way, way too big a breaker and part of this job is to switch that over to the circuit the outlets are on (as the cooktop just plugs in anyway and isn't direct-wired). It was just temporary until I solved the other problem. This has nothing do do with a not-broken tab on the outlet; the 14/3 red wire is capped and the live/neutral are connected as normal. Of COURSE this circuit should not be on a double-pole 15A as it's just two outlets on the island. To restate the problem: the breaker these outlets are connected to via the 14/3 is OFF nominally because when it's turned ON, the breaker trips immediately. At least, this is what my Klein ET310 tells me. Given that this is a double pole 15A I'm wondering if the installer somehow looped the live wiresss and effectively bypassed the breaker so that resetting the breaker effectively "shorts" the circuit. Thoughts?

Strange problem on double-pole 15 amp breaker/circuit

I live in BC, so this is about 120VAC house wiring. I have an island in the kitchen that has two outlets on it. It used to have an electric cooktop (before I installed a gas cooktop) and that 30amp circuit is now just used for running the illumination for the gas top. The two outlets are on another circuit and wired strangely; one just simply chains off the other so let's ignore that. The supply line is a 14/3 with the red capped and not energized (checked with Klein tester).

When I put in my ET310 transmitter and check the service panel I find the Klein beeps when I hover over a double-pole 15 amp breaker (which has only ONE lever). This breaker is OFF all the time and when I attempt to turn it ON, it shorts out, there's a spark in the panel (!) and the breaker immediately opens. This was the situation when we bought the house and as it never seemed to affect anything I just left it off, thinking someday I'll get to it...

So, the primary outlet in the island started to act erratically, shutting off and on for no reason so I decided to investigate and this is how I found that the Klein traces the circuit to this double-pole breaker. Now, I'm thinking that the guy wired this circuit incorrectly and effectively somehow looped the two phases on the 14/3. I haven't yet opened up the panel (this is difficult for stupid reasons) to see what's up but was hoping someone had an idea of what's going on here?


Thanks guys but I guess I wasn't as clear as I thought I was being. Forget the 30A circuit used for the few watts the cooktop illumination uses; I understand that 30A is way, way too big a breaker and part of this job is to switch that over to the circuit the outlets are on (as the cooktop just plugs in anyway and isn't direct-wired). It was just temporary until I solved the other problem. This has nothing do do with a not-broken tab on the outlet; the 14/3 red wire is capped and the live/neutral are connected as normal. Of COURSE this circuit should not be on a double-pole 15A as it's just two outlets on the island. To restate the problem: the breaker these outlets are connected to via the 14/3 is OFF nominally because when it's turned ON, the breaker trips immediately. At least, this is what my Klein ET310 tells me. Given that this is a double pole 15A I'm wondering if the installer somehow looped the live wiresss and effectively bypassed the breaker so that resetting the breaker effectively "shorts" the circuit. Thoughts?

Why is my double-pole 15 amp breaker/circuit tripping?

I live in BC, so this is about 120VAC house wiring. I have an island in the kitchen that has two outlets on it. It used to have an electric cooktop (before I installed a gas cooktop) and that 30amp circuit is now just used for running the illumination for the gas top. The two outlets are on another circuit and wired strangely; one just simply chains off the other so let's ignore that. The supply line is a 14/3 with the red capped and not energized (checked with Klein tester).

When I put in my ET310 transmitter and check the service panel I find the Klein beeps when I hover over a double-pole 15 amp breaker (which has only ONE lever). This breaker is OFF all the time and when I attempt to turn it ON, it shorts out, there's a spark in the panel (!) and the breaker immediately opens. This was the situation when we bought the house and as it never seemed to affect anything I just left it off, thinking someday I'll get to it...

So, the primary outlet in the island started to act erratically, shutting off and on for no reason so I decided to investigate and this is how I found that the Klein traces the circuit to this double-pole breaker. Now, I'm thinking that the guy wired this circuit incorrectly and effectively somehow looped the two phases on the 14/3. I haven't yet opened up the panel (this is difficult for stupid reasons) to see what's up but was hoping someone had an idea of what's going on here?


Thanks guys but I guess I wasn't as clear as I thought I was being. Forget the 30A circuit used for the few watts the cooktop illumination uses; I understand that 30A is way, way too big a breaker and part of this job is to switch that over to the circuit the outlets are on (as the cooktop just plugs in anyway and isn't direct-wired). It was just temporary until I solved the other problem. This has nothing do do with a not-broken tab on the outlet; the 14/3 red wire is capped and the live/neutral are connected as normal. Of COURSE this circuit should not be on a double-pole 15A as it's just two outlets on the island. To restate the problem: the breaker these outlets are connected to via the 14/3 is OFF nominally because when it's turned ON, the breaker trips immediately. At least, this is what my Klein ET310 tells me. Given that this is a double pole 15A I'm wondering if the installer somehow looped the live wiresss and effectively bypassed the breaker so that resetting the breaker effectively "shorts" the circuit. Thoughts?

Bumped by Community user
appended answer 291252 as supplemental
Source Link
Niall C.
  • 20.8k
  • 18
  • 95
  • 135

I live in BC, so this is about 120VAC house wiring. I have an island in the kitchen that has two outlets on it. It used to have an electric cooktop (before I installed a gas cooktop) and that 30amp circuit is now just used for running the illumination for the gas top. The two outlets are on another circuit and wired strangely; one just simply chains off the other so let's ignore that. The supply line is a 14/3 with the red capped and not energized (checked with Klein tester).

When I put in my ET310 transmitter and check the service panel I find the Klein beeps when I hover over a double-pole 15 amp breaker (which has only ONE lever). This breaker is OFF all the time and when I attempt to turn it ON, it shorts out, there's a spark in the panel (!) and the breaker immediately opens. This was the situation when we bought the house and as it never seemed to affect anything I just left it off, thinking someday I'll get to it...

So, the primary outlet in the island started to act erratically, shutting off and on for no reason so I decided to investigate and this is how I found that the Klein traces the circuit to this double-pole breaker. Now, I'm thinking that the guy wired this circuit incorrectly and effectively somehow looped the two phases on the 14/3. I haven't yet opened up the panel (this is difficult for stupid reasons) to see what's up but was hoping someone had an idea of what's going on here?


Thanks guys but I guess I wasn't as clear as I thought I was being. Forget the 30A circuit used for the few watts the cooktop illumination uses; I understand that 30A is way, way too big a breaker and part of this job is to switch that over to the circuit the outlets are on (as the cooktop just plugs in anyway and isn't direct-wired). It was just temporary until I solved the other problem. This has nothing do do with a not-broken tab on the outlet; the 14/3 red wire is capped and the live/neutral are connected as normal. Of COURSE this circuit should not be on a double-pole 15A as it's just two outlets on the island. To restate the problem: the breaker these outlets are connected to via the 14/3 is OFF nominally because when it's turned ON, the breaker trips immediately. At least, this is what my Klein ET310 tells me. Given that this is a double pole 15A I'm wondering if the installer somehow looped the live wiresss and effectively bypassed the breaker so that resetting the breaker effectively "shorts" the circuit. Thoughts?

I live in BC, so this is about 120VAC house wiring. I have an island in the kitchen that has two outlets on it. It used to have an electric cooktop (before I installed a gas cooktop) and that 30amp circuit is now just used for running the illumination for the gas top. The two outlets are on another circuit and wired strangely; one just simply chains off the other so let's ignore that. The supply line is a 14/3 with the red capped and not energized (checked with Klein tester).

When I put in my ET310 transmitter and check the service panel I find the Klein beeps when I hover over a double-pole 15 amp breaker (which has only ONE lever). This breaker is OFF all the time and when I attempt to turn it ON, it shorts out, there's a spark in the panel (!) and the breaker immediately opens. This was the situation when we bought the house and as it never seemed to affect anything I just left it off, thinking someday I'll get to it...

So, the primary outlet in the island started to act erratically, shutting off and on for no reason so I decided to investigate and this is how I found that the Klein traces the circuit to this double-pole breaker. Now, I'm thinking that the guy wired this circuit incorrectly and effectively somehow looped the two phases on the 14/3. I haven't yet opened up the panel (this is difficult for stupid reasons) to see what's up but was hoping someone had an idea of what's going on here?

I live in BC, so this is about 120VAC house wiring. I have an island in the kitchen that has two outlets on it. It used to have an electric cooktop (before I installed a gas cooktop) and that 30amp circuit is now just used for running the illumination for the gas top. The two outlets are on another circuit and wired strangely; one just simply chains off the other so let's ignore that. The supply line is a 14/3 with the red capped and not energized (checked with Klein tester).

When I put in my ET310 transmitter and check the service panel I find the Klein beeps when I hover over a double-pole 15 amp breaker (which has only ONE lever). This breaker is OFF all the time and when I attempt to turn it ON, it shorts out, there's a spark in the panel (!) and the breaker immediately opens. This was the situation when we bought the house and as it never seemed to affect anything I just left it off, thinking someday I'll get to it...

So, the primary outlet in the island started to act erratically, shutting off and on for no reason so I decided to investigate and this is how I found that the Klein traces the circuit to this double-pole breaker. Now, I'm thinking that the guy wired this circuit incorrectly and effectively somehow looped the two phases on the 14/3. I haven't yet opened up the panel (this is difficult for stupid reasons) to see what's up but was hoping someone had an idea of what's going on here?


Thanks guys but I guess I wasn't as clear as I thought I was being. Forget the 30A circuit used for the few watts the cooktop illumination uses; I understand that 30A is way, way too big a breaker and part of this job is to switch that over to the circuit the outlets are on (as the cooktop just plugs in anyway and isn't direct-wired). It was just temporary until I solved the other problem. This has nothing do do with a not-broken tab on the outlet; the 14/3 red wire is capped and the live/neutral are connected as normal. Of COURSE this circuit should not be on a double-pole 15A as it's just two outlets on the island. To restate the problem: the breaker these outlets are connected to via the 14/3 is OFF nominally because when it's turned ON, the breaker trips immediately. At least, this is what my Klein ET310 tells me. Given that this is a double pole 15A I'm wondering if the installer somehow looped the live wiresss and effectively bypassed the breaker so that resetting the breaker effectively "shorts" the circuit. Thoughts?

Split into paragraphs
Source Link
Rohit Gupta
  • 7.4k
  • 10
  • 26
  • 38

I live in BC, so this is about 120VAC house wiring. I have an island in the kitchen that has two outlets on it. It used to have an electric cooktop (before I installed a gas cooktop) and that 30amp circuit is now just used for running the illumination for the gas top. The two outlets are on another circuit and wired strangely; one just simply chains off the other so let's ignore that. The supply line is a 14/3 with the red capped and not energized (checked with Klein tester). 

When I put in my ET310 transmitter and check the service panel I find the Klein beeps when I hover over a double-pole 15 amp breaker (which has only ONE lever). This breaker is OFF all the time and when I attempt to turn it ON, it shorts out, there's a spark in the panel (!) and the breaker immediately opens. This was the situation when we bought the house and as it never seemed to affect anything I just left it off, thinking someday I'll get to it... 

So, the primary outlet in the island started to act erratically, shutting off and on for no reason so I decided to investigate and this is how I found that the Klein traces the circuit to this double-pole breaker. Now, I'm thinking that the guy wired this circuit incorrectly and effectively somehow looped the two phases on the 14/3. I haven't yet opened up the panel (this is difficult for stupid reasons) to see what's up but was hoping someone had an idea of what's going on here?

I live in BC, so this is about 120VAC house wiring. I have an island in the kitchen that has two outlets on it. It used to have an electric cooktop (before I installed a gas cooktop) and that 30amp circuit is now just used for running the illumination for the gas top. The two outlets are on another circuit and wired strangely; one just simply chains off the other so let's ignore that. The supply line is a 14/3 with the red capped and not energized (checked with Klein tester). When I put in my ET310 transmitter and check the service panel I find the Klein beeps when I hover over a double-pole 15 amp breaker (which has only ONE lever). This breaker is OFF all the time and when I attempt to turn it ON, it shorts out, there's a spark in the panel (!) and the breaker immediately opens. This was the situation when we bought the house and as it never seemed to affect anything I just left it off, thinking someday I'll get to it... So, the primary outlet in the island started to act erratically, shutting off and on for no reason so I decided to investigate and this is how I found that the Klein traces the circuit to this double-pole breaker. Now, I'm thinking that the guy wired this circuit incorrectly and effectively somehow looped the two phases on the 14/3. I haven't yet opened up the panel (this is difficult for stupid reasons) to see what's up but was hoping someone had an idea of what's going on here?

I live in BC, so this is about 120VAC house wiring. I have an island in the kitchen that has two outlets on it. It used to have an electric cooktop (before I installed a gas cooktop) and that 30amp circuit is now just used for running the illumination for the gas top. The two outlets are on another circuit and wired strangely; one just simply chains off the other so let's ignore that. The supply line is a 14/3 with the red capped and not energized (checked with Klein tester). 

When I put in my ET310 transmitter and check the service panel I find the Klein beeps when I hover over a double-pole 15 amp breaker (which has only ONE lever). This breaker is OFF all the time and when I attempt to turn it ON, it shorts out, there's a spark in the panel (!) and the breaker immediately opens. This was the situation when we bought the house and as it never seemed to affect anything I just left it off, thinking someday I'll get to it... 

So, the primary outlet in the island started to act erratically, shutting off and on for no reason so I decided to investigate and this is how I found that the Klein traces the circuit to this double-pole breaker. Now, I'm thinking that the guy wired this circuit incorrectly and effectively somehow looped the two phases on the 14/3. I haven't yet opened up the panel (this is difficult for stupid reasons) to see what's up but was hoping someone had an idea of what's going on here?