Skip to main content
7 events
when toggle format what by license comment
Dec 21, 2023 at 17:34 comment added manassehkatz-Moving 2 Codidact That is an old-style/feeder type of cable. Which if it is sized OK for 40A (minimum 8 AWG, and that looks like it is OK) then used to be fine for 3-wire, so now the issue is adding a ground wire and then connecting to a modern (4-prong) receptacle while making sure neutral and ground don't connect to each other in the receptacle box.
Dec 21, 2023 at 17:20 comment added Shannon4570 Hi - thanks for the reply. Like I said, please ignore the white tape. I want to be sure I am clear here - the SE cable goes directly from my main panel to the receptacle box. It is black, black with red stripe and bare neutral. In my main panel, all neutrals and grounds go to the same bus. I want to do whatever is correct and safe.
Dec 21, 2023 at 17:02 comment added manassehkatz-Moving 2 Codidact touch the panel box itself and therefore becomes a ground - but ground and neutral need to be separate because it isn't a main panel any more. But assuming it terminates in an actual main panel then that's OK and you just need a separate ground wire - but which needs to be kept electrically separate from the bare neutral in the junction box - simplest way may be to use a green wire rather than bare.
Dec 21, 2023 at 17:01 comment added manassehkatz-Moving 2 Codidact No, it is really # 3. Black + Black/Red (I think) with white tape (why??? That's just wrong!) + bare. The key is that the 3rd wire is bare but not a typical ground. That cable is really meant for subpanel feeder or similar in the pre-ground days. The trick being that you have to make sure that bare neutral doesn't get grounded along the way. Simply example: If you had a main panel (neutral ground bonded) and then made it a subpanel (either new, larger, main or replaced outside meter with meter-main) then if the bare neutral is in a metal box (like the main-now-subpanel box) it is presumed to
Dec 21, 2023 at 16:54 comment added Shannon4570 Actually I was incorrect. My wiring matches bullet 2, not 3. There is a black, red and bare /white neutral.
Dec 21, 2023 at 16:14 comment added Shannon4570 Thanks for the great response. For clarification: We bought the house from the original owner with the original stove. Wiring was originally 3 prong. The service wiring to the receptacle from the panel matches your 3rd bullet.
Dec 21, 2023 at 2:32 history answered manassehkatz-Moving 2 Codidact CC BY-SA 4.0