Skip to main content
deleted 3 characters in body
Source Link
popham
  • 10.6k
  • 1
  • 18
  • 33

You'll need an engineer for this. Wind load is going to determine the design. Canopy wind loads fall under 30.11 from ASCE 7-16. Once you have a wind psf, then the exterior deck section from the IRC tables can provide your framing sizes, where you could substitute 0.75(20psf)+0.75(0.6)(wind psf) for the tabulated snow psf.

My wild guess is that a 10 psf dead load plus 30 psf snow load under IRC R507rafter tables provides sufficient framing for your patio cover. 10 psf dead load plus 5040 psf snowlive load wouldunder IRC R507 should yield a conservative design.

You'll probably need a load path down to the foundation for resisting uplift, too. Typical deck details will get you 90% there (toe nails in joist hangers and notched post connections with 2 bolts each), but the post bases will probably need some tension detailing.

You'll need an engineer for this. Wind load is going to determine the design. Canopy wind loads fall under 30.11 from ASCE 7-16. Once you have a wind psf, then the exterior deck section from the IRC can provide your framing sizes, where you could substitute 0.75(20psf)+0.75(0.6)(wind psf) for the tabulated snow psf.

My wild guess is that a 10 psf dead load plus 30 psf snow load under IRC R507 provides sufficient framing for your patio cover. 10 psf dead load plus 50 psf snow load would yield a conservative design.

You'll probably need a load path down to the foundation for resisting uplift, too. Typical deck details will get you 90% there (toe nails in joist hangers and notched post connections with 2 bolts each), but the post bases will need some tension detailing.

You'll need an engineer for this. Wind load is going to determine the design. Canopy wind loads fall under 30.11 from ASCE 7-16. Once you have a wind psf, then IRC tables can provide your framing sizes, where you could substitute 0.75(20psf)+0.75(0.6)(wind psf) for the tabulated snow psf.

My wild guess is that a 10 psf dead load plus 30 psf snow load under IRC rafter tables provides sufficient framing for your patio cover. 10 psf dead load plus 40 psf live load under IRC R507 should yield a conservative design.

You'll probably need a load path down to the foundation for resisting uplift, too. Typical deck details will get you 90% there (toe nails in joist hangers and notched post connections with 2 bolts each), but the post bases will probably need some tension detailing.

added 260 characters in body
Source Link
popham
  • 10.6k
  • 1
  • 18
  • 33

You'll need an engineer for this. Wind load is going to determine the design. Canopy wind loads fall under 30.11 from ASCE 7-16. Once you have a wind psf, then the exterior deck section from the IRC can provide your framing sizes, where you could substitute 0.75(20psf)+0.75(0.6)(wind psf) for the tabulated snow psf.

My wild guess is that a 10 psf dead load plus 30 psf snow load under IRC R507 provides sufficient framing for your patio cover. 10 psf dead load plus 50 psf snow load would yield a conservative design.

You'll probably need a load path down to the foundation for resisting uplift, too. Typical deck details will get you 90% there (toe nails in joist hangers and notched post connections with 2 bolts each), but the post bases will need some tension detailing.

You'll need an engineer for this. Wind load is going to determine the design. Canopy wind loads fall under 30.11 from ASCE 7-16. Once you have a wind psf, then the exterior deck section from the IRC can provide your framing sizes, where you could substitute 0.75(20psf)+0.75(0.6)(wind psf) for the tabulated snow psf.

My wild guess is that a 10 psf dead load plus 30 psf snow load under IRC R507 provides sufficient framing for your patio cover. 10 psf dead load plus 50 psf snow load would yield a conservative design.

You'll need an engineer for this. Wind load is going to determine the design. Canopy wind loads fall under 30.11 from ASCE 7-16. Once you have a wind psf, then the exterior deck section from the IRC can provide your framing sizes, where you could substitute 0.75(20psf)+0.75(0.6)(wind psf) for the tabulated snow psf.

My wild guess is that a 10 psf dead load plus 30 psf snow load under IRC R507 provides sufficient framing for your patio cover. 10 psf dead load plus 50 psf snow load would yield a conservative design.

You'll probably need a load path down to the foundation for resisting uplift, too. Typical deck details will get you 90% there (toe nails in joist hangers and notched post connections with 2 bolts each), but the post bases will need some tension detailing.

Source Link
popham
  • 10.6k
  • 1
  • 18
  • 33

You'll need an engineer for this. Wind load is going to determine the design. Canopy wind loads fall under 30.11 from ASCE 7-16. Once you have a wind psf, then the exterior deck section from the IRC can provide your framing sizes, where you could substitute 0.75(20psf)+0.75(0.6)(wind psf) for the tabulated snow psf.