Sep 29, 2023 at 18:45 | comment | added | Mazura | There's an actual ground fault or you're stealing a neutral. | |
Sep 29, 2023 at 16:51 | answer | added | Harper - Reinstate Monica | timeline score: 2 | |
Sep 29, 2023 at 14:23 | history | became hot network question | |||
Sep 29, 2023 at 14:14 | comment | added | Ecnerwal | Does the ground wire coming in with the service wires connect to a suitable local grounding system, such as a pair of rods at least 8 feet apart? | |
Sep 29, 2023 at 14:00 | comment | added | Ecnerwal | See also: diy.stackexchange.com/a/271931/18078 | |
Sep 29, 2023 at 13:55 | answer | added | Ecnerwal | timeline score: 8 | |
Sep 29, 2023 at 11:47 | comment | added | ThreePhaseEel | Can we have photos of the rest of the label you posted a partial photo of please? | |
Sep 29, 2023 at 11:10 | history | edited | FreeMan | CC BY-SA 4.0 |
edited title
|
Sep 29, 2023 at 10:59 | history | edited | FreeMan | CC BY-SA 4.0 |
deleted 78 characters in body
|
Sep 29, 2023 at 10:48 | comment | added | nobody | GFCI breakers and receptacles come with printed instructions that will tell you very specifically how to install them. Did you read the instructions? | |
Sep 29, 2023 at 5:40 | history | edited | Rohit Gupta | CC BY-SA 4.0 |
added 9 characters in body
|
Sep 29, 2023 at 4:28 | comment | added | manassehkatz-Moving 2 Codidact | Are there any other buildings served by the same utility service? Or is the meter on the power pole only serving this garage? | |
Sep 29, 2023 at 4:19 | answer | added | manassehkatz-Moving 2 Codidact | timeline score: 8 | |
Sep 29, 2023 at 4:02 | comment | added | popham | If your problem is probably with the white pigtail wire, then you should post a photo of how precisely you've been configuring it. | |
Sep 29, 2023 at 4:00 | comment | added | popham | Your question title should clarify whether this is a main panel (directly fed by a meter) or a subpanel (directly fed by a main panel somewhere else). You say that it comes directly from a power pole, so maybe it's a main panel. Is the line on that power pole coming from the power company or from a main panel on your property? The ground and neutral buses in a main panel should be bonded like they appear to be, so if this is a main panel, then it's okay. | |
Sep 29, 2023 at 3:54 | comment | added | ThreePhaseEel | Can you post photos of the labeling on the inside left and right of the panel cabinet please? | |
Sep 29, 2023 at 3:53 | history | edited | Chip | CC BY-SA 4.0 |