Sep 25, 2023 at 18:38 comment added Caleb Murphy I would treat it as a sub panel ran off of a 100 amp breaker from the main panel ran through conduit underground to my metal shop 20 feet away where I would set up a separate panel with its own integrated shut off. I would also install ground rods off the sub panel.
Sep 25, 2023 at 13:04 comment added Huesmann Wait, "at the meter which is where I would run off of" meaning this isn't actually a subpanel?
Sep 24, 2023 at 15:56 comment added nobody How much load do you actually want to put in the sub-panel? It's perfectly legal to feed a panel rated for "X" amps with a breaker smaller than "X" (and corresponding smaller wire). The rating is a maximum, not a level you're required to achieve. You may not have load-calculation capacity for an extra 100A, 90A wire can be significantly less expensive than 100A wire, etc.
Sep 24, 2023 at 15:51 history edited nobody
edited tags
Sep 24, 2023 at 15:46 answer added manassehkatz-Moving 2 Codidact timeline score: 2
Sep 24, 2023 at 15:30 comment added manassehkatz-Moving 2 Codidact Thank you. There is a special rule when a subpanel feed is equal to the main feed, but that does not apply here.
Sep 24, 2023 at 15:27 comment added Caleb Murphy 200 amp main service at the meter which is where I would run off of.
Sep 24, 2023 at 15:04 comment added manassehkatz-Moving 2 Codidact What is the main service feed ampacity?
S Sep 24, 2023 at 14:54 review First questions
Sep 24, 2023 at 19:42
S Sep 24, 2023 at 14:54 history asked Caleb Murphy CC BY-SA 4.0