Timeline for Wiring for water heater and dryer
Current License: CC BY-SA 4.0
12 events
when toggle format | what | by | license | comment | |
---|---|---|---|---|---|
May 28, 2023 at 10:30 | vote | accept | user162793 | ||
May 26, 2023 at 21:33 | comment | added | Ecnerwal | You need white or gray for the neutral wire at this wire size. The hots can be all one color and tape marked, or two colors to make it easier. If using two colors, use e.g. red for both hots of one circuit, black for both hots of the other. Or pink, blue, orange... Your revised plan appears workable. | |
May 26, 2023 at 21:13 | comment | added | user162793 | Answer my last question: I think they can be same color per diy.stackexchange.com/questions/209735 Just need to use tape to wrap each pair. | |
May 26, 2023 at 21:06 | comment | added | user162793 | Do the THHN wires between circuits need to be different color? Can I have 2 black, 2 red, 1 white in the EMT and then it's up to me to make sure I wire them to the proper circuit? | |
May 26, 2023 at 18:32 | comment | added | user162793 | I edited my question with my plan. Please let me know if that looks good. | |
May 26, 2023 at 1:35 | comment | added | Ecnerwal | Sharing the ground is normal and unremarkable. GFCIs do not look at ground. One suitable for a 240V dryer compares current on the two hots and neutral for the dryer. If they don't add up, that's a ground fault - no need to actually look at ground, and GFCIs will work on ungrounded circuits because that's how they work. | |
May 26, 2023 at 1:31 | comment | added | Ecnerwal | Complete, correctly connected non-flex metallic conduit is a ground conductor - so you don't need a grounding wire in it (that's why 5, not 6 wires - two hots for the charger, plus 2 hots and 1 neutral for the dryer, conduit itself as ground) and then you connect a pigtail to the grounding screw hole on the metallic box where the device is. The correctly tightened metallic connectors (and removal of paint if you don't use ones that are designed to break through the paint themselves) connects the conduit to the grounded panel or sub-panel. | |
May 25, 2023 at 19:25 | comment | added | user162793 | Can I share ground between a GFCI and non GFCI circuit? EMT seems much cheaper. If I go with 5 10 AWG in 1/2" EMT, how do I ground the conduit? I will need a junction boxes and not conduit bodies, right? I'm thinking a junction box above the panels to attach the ground wire. No splicing in the box. Another box again without any splicing to the top left to route the 3 wires to the dryer outlet and the 2 wires plus a new ground to the water heater via a flexible conduit. Or is there a way to ground conduit bodies? | |
May 25, 2023 at 18:04 | history | edited | NoSparksPlease | CC BY-SA 4.0 |
Change to NEC recognized raceway type
|
May 25, 2023 at 13:47 | history | edited | Ecnerwal | CC BY-SA 4.0 |
added 565 characters in body
|
May 25, 2023 at 13:42 | history | edited | Ecnerwal | CC BY-SA 4.0 |
added 565 characters in body
|
May 25, 2023 at 13:30 | history | answered | Ecnerwal | CC BY-SA 4.0 |