Timeline for Wiring mini split external and internal
Current License: CC BY-SA 4.0
5 events
when toggle format | what | by | license | comment | |
---|---|---|---|---|---|
May 10, 2023 at 0:42 | comment | added | user903805 | I was looking tonight at a unit with a 24k BTU compared to the 18k than I was originally thinking and When checking the 24k manual it says: MCA:22 amps, MOP:35 amps. Minimum wire gauge for power cables: 8 min, 6 preferred. I’m guessing that means I have to run 8 gauge wire off a 40amp main breaker with a 35 amp breaker in the subpanel because the 10 gauge wire and 30amp I have now is below MOP? | |
May 9, 2023 at 19:03 | comment | added | Harper - Reinstate Monica | @user903805 Yeah, that's fine. | |
May 9, 2023 at 16:36 | comment | added | user903805 | If I put the sub panel outside: 30amp breaker, 10 gauge wire, out the wall, into sub panel, then dual 20 amp breakers, can I send the wire back inside for my air compressor? | |
May 8, 2023 at 20:10 | comment | added | keshlam | I'm my case, an existing outdoor outlet covered that last requirement. | |
May 8, 2023 at 19:11 | history | answered | Harper - Reinstate Monica | CC BY-SA 4.0 |