May 21, 2023 at 12:52 history edited Ecnerwal CC BY-SA 4.0
deleted 55 characters in body
May 5, 2023 at 21:01 comment added peter Also for context, it's a plug-on neutral panel (as you noted). In hindsight, this probably contributed to misunderstanding it as "I don't need to worry about neutrals for AFCI breakers here". But I guess that's only for the pigtail, not the branch circuit neutral.
May 5, 2023 at 20:59 comment added peter Yes! Fridge (and all other appliances) work perfectly fine. I feel like an idiot, but also, I've never been so glad to feel like an idiot in my life. I was in the process of returning the fridge and buying another one, and was considering some deeper investigation on the in-wall wiring.
May 5, 2023 at 20:58 vote accept peter
May 5, 2023 at 20:56 comment added Ecnerwal When shooting in the dark I try to cover many bases, since I don't know which one might be right until I have more information. Does the fridge work now?
May 5, 2023 at 20:55 comment added peter p.s. it wasn't a MWBC, these are two completely independent circuits each with their own breakers. I've installed a different CAFCI breaker for each of them now.
May 5, 2023 at 20:54 comment added peter This was it! This was my first work with AFCI breakers and I didn't realize I had to connect the branch circuit neutral to the breaker too. After your answer I went and found the matching neutral and hooked it up to the breaker, and since then it no longer trips even with loads connected. Thank you!
May 5, 2023 at 19:54 comment added Chris O Good catch on the neutral.
May 5, 2023 at 18:59 history edited Ecnerwal CC BY-SA 4.0
added 174 characters in body
May 5, 2023 at 18:52 history answered Ecnerwal CC BY-SA 4.0