Jul 30, 2022 at 21:51 comment added Ed Beal Emir you can use a double pole but it is a waste there are tie bars and you will see they come in 2 pole or 3 pole , using them in 2 pole would be more expensive but they do come in smaller amperage’s as control panels use 1,2,3amp etc where in power wiring for 220v we use 15& 20 I think in the future there will be 10 amp for copper coated aluminum on lighting circuits.
Jul 30, 2022 at 19:53 comment added Emir I think we are mixing the boxes here. I was refering to the miniature breaker (the white ones) As i mentioned above, i think i understood the basics of the Box with the Black breakers, my question is about the the DIN Rail. How could you make a two live lines connection if those breakers have a Neutral and one Line only, thanks
Jul 30, 2022 at 19:00 comment added Ed Beal Emir there are different types like GFCI’s that have a neutral connection these do not connect to the hot buss. With some the neutral is a snap connection similar to the hot but at the opposite end of the breaker.
Jul 30, 2022 at 18:46 comment added Emir Even if the breaker has a N (neutral) on one side, you can connect the second live line there? I just want to be 100% sure, thanks
Jul 30, 2022 at 14:58 comment added Ed Beal The neutral is not going to a breaker buss. In a main panel it is going to the “silver long buss” that connects with the ground all the neutrals and ground connect at the same point in a main panel. The same is true for DIN you only need the breaker for the 2 hots the neutral and ground have a common buss
Jul 29, 2022 at 23:01 comment added Emir But how, if you have the two live lines wires +neutral, how would you make the connection using the rail ones, two breaker? One breaker for line 1,second breaker for line 2, in that how can you distribute that to let's, say a 220 A/C, thanks for your answer
Jul 29, 2022 at 19:44 history answered Ed Beal CC BY-SA 4.0