Nov 15, 2023 at 17:02 | answer | added | Richard R | timeline score: 3 | |
Jan 24, 2022 at 15:26 | answer | added | maples | timeline score: 3 | |
Oct 25, 2021 at 16:08 | history | edited | maples | CC BY-SA 4.0 |
add additional info
|
Oct 25, 2021 at 9:58 | vote | accept | maples | ||
Oct 25, 2021 at 2:17 | comment | added | maples | @ThreePhaseEel done :) | |
Oct 25, 2021 at 2:16 | history | edited | maples | CC BY-SA 4.0 |
add photo
|
Oct 25, 2021 at 1:28 | comment | added | ThreePhaseEel | @maples -- can you post photos of the breaker panel in question please? | |
Oct 25, 2021 at 1:12 | history | edited | maples | CC BY-SA 4.0 |
added 76 characters in body
|
Oct 25, 2021 at 1:03 | history | edited | maples | CC BY-SA 4.0 |
updates in response to comments
|
Oct 25, 2021 at 0:58 | comment | added | maples | Just added some updates in response to your comments, thanks everyone! | |
Oct 25, 2021 at 0:58 | history | edited | maples | CC BY-SA 4.0 |
updates in response to comments
|
Oct 24, 2021 at 17:48 | comment | added | Harper - Reinstate Monica | Go to the circuit panel and turn OFF all 240V (2-pole) breakers (not the main). Yes, really. Turn them off, even if the appliance is already non-functional. Water heater, range, dryer, A/C, etc. Now tell me the status of the "weak circuits". Are they dead as a stone now? | |
Oct 24, 2021 at 12:54 | answer | added | NoSparksPlease | timeline score: 4 | |
Oct 24, 2021 at 12:48 | comment | added | A. I. Breveleri | There's one "dual" breaker...that is physically loose in the breaker box...and the label is crossed out, so I guess it's unused - If it has wires attached to it, it is almost certainly not "unused", and if it is in use, it is probably the cause of the symptoms you describe. | |
Oct 24, 2021 at 12:42 | comment | added | crip659 | As this is a rental, about the only thing you do on your own is changing light bulbs. Everything else must be done by a licensed electrician hired by the landlord. The power company only checked their stuff to the meter, pass the meter is the owners problem. | |
S Oct 24, 2021 at 12:25 | review | First questions | |||
Oct 24, 2021 at 12:32 | |||||
S Oct 24, 2021 at 12:25 | history | asked | maples | CC BY-SA 4.0 |