Sep 1, 2021 at 1:51 comment added ThreePhaseEel What size is this shed, in square feet?
Aug 31, 2021 at 20:19 history edited Machavity
edited tags
Aug 31, 2021 at 19:59 comment added George Anderson Unless this is being feed directly off a meter base (like a class 320 in which case it'd need to AL 4/0 for the hots and 2/0 for the neutral), let's not forget to mention this needs to be a 4 wire feed (2 hots, neutral and ground), neutral and ground NOT bonded and local grounding rods at the shed. Assuming fed from another panel, breaker size needs to be appropriate for wire size and the sub-panel in the shed needs to rated for at least the over-current protection, going oversize on the panel is not an issue, going under size is.
Aug 31, 2021 at 19:19 answer added Harper - Reinstate Monica timeline score: 3
Aug 31, 2021 at 18:58 answer added NoSparksPlease timeline score: 1
Aug 31, 2021 at 18:35 comment added NoSparksPlease Is the 25A the "minimum circuit ampacity", "maximum overcurrent protection", or some other number? We really need to know the minimum circuit ampacity to figure the minimum, even though you will get recommendations to not do the minimum.
Aug 31, 2021 at 16:24 history edited isherwood CC BY-SA 4.0
edited body; edited title
Aug 31, 2021 at 16:07 comment added NoSparksPlease How far is shed from source panel?
Aug 31, 2021 at 15:36 comment added CommunityBot Please clarify your specific problem or provide additional details to highlight exactly what you need. As it's currently written, it's hard to tell exactly what you're asking.
Aug 31, 2021 at 15:29 comment added Micah Montoya Welcome. Code varies by jurisdiction. Where you are located?
S Aug 31, 2021 at 15:13 review First questions
Aug 31, 2021 at 15:36
S Aug 31, 2021 at 15:13 history asked Berrae Meixsell CC BY-SA 4.0