when toggle format | what | by | license | comment | |
---|---|---|---|---|---|
May 22, 2021 at 2:37 | comment | added | Stanwood | @NoSparksPlease The two panels (or cabinets) are connected by a few inches of non-metallic grey PVC conduit. While I have not opened the utility seal to look inside I have good reason to assume that the metal cabinet housing the meter is bonded to the service neutral. It would be unsafe to leave it floating. That neutral wire is bonded to the house ground at my service panel. | |
May 22, 2021 at 2:00 | vote | accept | Stanwood | ||
May 22, 2021 at 1:46 | answer | added | ThreePhaseEel | timeline score: 1 | |
May 21, 2021 at 17:13 | comment | added | Harper - Reinstate Monica | Here's the thing. Meters are not inherently grounded. Generally they pick up ground via use of metal conduit connecting them to the service panel. However you say yours is non metallic. Unfortunate. | |
May 21, 2021 at 13:05 | comment | added | Phil Freedenberg | Verizon installed my FIOS ONT with ground wire clipped to the meter box. Dominion is my utility as well. | |
May 21, 2021 at 5:20 | comment | added | NoSparksPlease | What is NM conduit? Non-metallic conduit? Not a code recognized type. I'm having a difficult time understanding what a "meter panel" is and how if you mean "meter cabinet" how it is grounded if connected by some nonmetallic piping to the service panel. | |
May 21, 2021 at 4:32 | comment | added | Stanwood | Dominion Energy (Virginia) | |
May 21, 2021 at 4:30 | comment | added | ThreePhaseEel | Who's your electric utility? | |
May 21, 2021 at 3:58 | history | asked | Stanwood | CC BY-SA 4.0 |