Mar 9, 2021 at 14:29 comment added jay613 Safety problems with both. I'll elaborate in an Answer.
Mar 9, 2021 at 14:06 comment added user2285215 yes @jay613 you are correct, thermostat wire comes from right side of the box, which is a (conduit?) going up to the ceiling > lightbulb/socket > wall. Is the safety issue pertaining to me "adding a C-wire" or just how its currently wired? heh
Mar 9, 2021 at 10:28 comment added jay613 Just to reopen this can of copper worms, I think the thermostat wire enters through the EMT on the top right side of the cutoff box, the same EMT as the power source. I think the green is already connected to neutral! Ironic. But this doesn't change the outcome ... It should be redone by an electrician as there are serious safety issues here.
Mar 9, 2021 at 4:05 vote accept user2285215
Mar 9, 2021 at 3:55 comment added ThreePhaseEel @user2285215 -- we thank people around here by upvoting and/or accepting their answers :)
Mar 9, 2021 at 3:35 comment added user2285215 Thanks for your reply. Ive added a couple of photos of the thermostat wires. Based on your input I suspect that this is something more than I can handle. I was hoping to avoid plugging in a 24VAC transformer
Mar 9, 2021 at 3:27 comment added jay613 Given the way the low voltage wires fold back into the junction box, I don't think we know for sure how the pressuretrol is wired but I agree with the advice, this boiler deserves a look by someone knowledgeable.
Mar 9, 2021 at 3:03 comment added ThreePhaseEel Sidenote: if you can't find a steam boiler expert in your area, (and even perhaps if you can), you'll probably want to read Dan Holohan's We Got Steam Heat for more advice on your system overall -- steam systems behave very differently from forced-air, and applying forced-air logic to steam systems can be quite counterproductive as a result