Jan 5, 2021 at 23:34 comment added ThreePhaseEel @Eli -- that panel should suit quite nicely for your garage :) and using SER for the interior runs with the Polaris-type connectors will work (note that if you want to run the copper in the underground conduit at 90degC, you'll need 90degC connectors in the pull boxes -- most Polaris-type connectors are indeed rated to run that hot, but some aren't, so pay attention to the specs on what you buy if you do that)
Jan 5, 2021 at 14:34 comment added Eli The 150A panel is a Cutler-Hammer (Eaton) BR3030B150. I'll likely stick with the 60A service as you described, but if I did want to go up to 70A, would it be permissible (and not inadvisable) to use 3 or 2 GA SER Aluminum cable to make the interior runs, assuming all relevant components were CU/AL rated and no-ox is used at the connections? I would use a split bolt (wraped with splice tape then plastic tape) or Polaris type splice at either end of the conduit.
Jan 5, 2021 at 1:41 comment added ThreePhaseEel @Harper-ReinstateMonica -- not quite. 250.122(B) only applies when a conductor is upsized from the minimum required for a given ampacity, and Table 250.122 is based on the OCPD setting, not the wire ampacity
Jan 4, 2021 at 12:36 history edited ThreePhaseEel CC BY-SA 4.0
fix 75degC ampacity
Jan 4, 2021 at 6:31 comment added Harper - Reinstate Monica Wait, for 75C #6 copper, I get 65A out of that table. That also has an impact on the ground wire. Since the wire is capable of >60A, the ground must be too, i.e. #8
Jan 4, 2021 at 2:08 comment added ThreePhaseEel @Eli -- btw, as a crosscheck, what make/model is said 150A panel?
Jan 4, 2021 at 2:07 vote accept Eli
Jan 3, 2021 at 23:56 comment added ThreePhaseEel @Eli -- exactly, the size of the main breaker in the garage subpanel doesn't matter provided it's not the "weakest link" in the circuit, a job that's reserved for the feeder breaker in the main panel
Jan 3, 2021 at 23:50 comment added Eli Thank you, that was very informative! I already have a 150A main panel that was removed when I had the service upgraded to 200A, so ideally I can use that. One follow-up question on that, can I leave the 150 main breaker in that panel to use as a disconnect in the garage, provided that the feeder circuit is protected at the main service panel with an appropriately sized breaker?
Jan 3, 2021 at 21:30 history answered ThreePhaseEel CC BY-SA 4.0