Skip to main content
12 events
when toggle format what by license comment
Oct 7, 2020 at 23:57 comment added ThreePhaseEel @Ecnerwal -- yeah, metal well casings are right up there with Ufers in being amazing grounding electrodes as I understand it, and yes -- definitely worthwhile in any pour as long as you aren't in an awkward situation where everything's atop poly (which ruins all your work)
Oct 7, 2020 at 23:43 comment added Ecnerwal Pretty much bothering to connect a cable to your rebar, and ideally connect your rebar to the rest of your rebar (which you want to do for structural reasons anyway.) Your concrete and/or rebar suppliers should be familiar with what's needed - I think it's 4AWG cable and a connector suited to the job. Which is why it's something you should always do when pouring concrete - so little extra investment, for the best grounding electrode.
Oct 7, 2020 at 23:24 comment added D A my plan is to lay steel mesh and then #4 rebar spaced making 3' squares and all this raised 1" off the ground with small concrete couches that I have made. I guess I need to understand more of what an Ufer ground is.
Oct 7, 2020 at 17:23 comment added Ecnerwal Too bad the well casings appear to be PVC. My 100 foot x 8 inch steel ground rod is "da bomb" (but I also have 5 rods and a bunch of cable below 3 feet ;-)
Oct 7, 2020 at 17:08 comment added Harper - Reinstate Monica @Ecnerwal I think OP was just thinking of a normal copper ground rod set into the ground, installed before pour... yes an Ufer will engage the entire re-rod network.
Oct 7, 2020 at 16:40 comment added Ecnerwal And if there isn't add some. Concrete is expensive, steel is cheap, and steel makes concrete so much stronger... An 8 foot rod is not sufficient - you need 20 feet for a concrete encased electrode. So one hunk of full-length rebar is "adequate" but having your rebar properly tied to the rest will involve more than that one hunk of rebar in the system.
Oct 7, 2020 at 16:33 history edited Harper - Reinstate Monica CC BY-SA 4.0
added 636 characters in body
Oct 7, 2020 at 16:29 comment added Harper - Reinstate Monica @DA If there will be any steel re-rod in the pour, then by all means have them provide you an Ufer ground. That is the best ground rod in the world. Never do a pour without Ufers!
Oct 7, 2020 at 10:26 vote accept D A
Oct 7, 2020 at 10:26 vote accept D A
Oct 7, 2020 at 10:26
Oct 7, 2020 at 10:25 comment added D A I’ll remove the existing and pull a new 4-4-4-8 feed. And I’ll go with a 200amp service panel and nix the outside shutoff. And I’ll also get an 8’ bare copper ground rod in the slab before the pour.
Oct 7, 2020 at 1:49 history answered Harper - Reinstate Monica CC BY-SA 4.0