Aug 6, 2020 at 11:41 comment added ThreePhaseEel It's a figure of speech for having to maintain a hard division between the two sets of neutrals -- you can't cross the streams here, or else you'll create EMI and the risk of overloading a neutral wire
Aug 6, 2020 at 4:44 comment added Merlin -they-them- @ThreePhaseEel what is that wall? I Googled it but didn't find anything.
Aug 5, 2020 at 23:22 comment added ThreePhaseEel Yes, that's fine, as long as you maintain a "Chinese wall" between the two sets of neutrals in the box
Aug 5, 2020 at 17:32 vote accept Merlin -they-them-
Aug 5, 2020 at 17:31 comment added Merlin -they-them- @threePhaseEel I plan on connecting the outdoor light in the same gang box but I'll bring in a new cable from the breaker. Is that allowed to have 2 cables coming in from the breaker in the same gang box?
Aug 5, 2020 at 4:56 answer added Harper - Reinstate Monica timeline score: 4
Aug 5, 2020 at 2:18 comment added ThreePhaseEel What color is the status light on the Caseta? Also, where are you planning to connect to this different circuit at?