21 events
when toggle format what by license comment
S Jul 22 '20 at 0:54 history suggested Vikki CC BY-SA 4.0
Removing Extraneous Capitalisation.
Jul 21 '20 at 23:44 review Suggested edits
S Jul 22 '20 at 0:54
Jul 21 '20 at 15:34 comment added Eric Hauenstein This is a well-asked, very well-illustrated question. Kudos to you.
Jul 21 '20 at 11:35 comment added FreeMan Good thing you decided to test this now instead of waiting for hurricane season. Much better to figure this out now than when you're wet, wind blown, and all the stores are closed!
Jul 21 '20 at 11:29 history edited FreeMan CC BY-SA 4.0
Spell check, formatting
Jul 21 '20 at 9:00 history tweeted twitter.com/StackDIY/status/1285499773290676231
Jul 21 '20 at 4:51 history became hot network question
Jul 21 '20 at 4:27 history edited Ron CC BY-SA 4.0
added 92 characters in body
Jul 21 '20 at 3:05 history edited Machavity CC BY-SA 4.0
edited tags
Jul 21 '20 at 2:22 answer Harper - Reinstate Monica timeline score: 18
Jul 21 '20 at 1:54 comment added Harper - Reinstate Monica Oh, that’s the wrong answer. Assuming generator unplugged, that should be infinity. Found your problem!
Jul 21 '20 at 0:41 comment added Ron Curiosity got to me so I convinced everyone I had an emergency and I need to turn off the power I took ohms measurement on the backfeed breaker while on and the rest including main line off. and the OHMS read from 1.3 to a steady 1.
Jul 20 '20 at 23:58 comment added Ron It trips instantly after flipping on the backfeed breaker all other breakers in panel are off. I will measure the OHMS as soon as I can, right now everyone is home with Utility power and I will be screamed at if I turn everything off.
Jul 20 '20 at 23:48 history edited Ron CC BY-SA 4.0
added 75 characters in body
Jul 20 '20 at 23:30 comment added ThreePhaseEel Does the breaker on the generator trip instantly when reset, or does it stay on for a little bit then trip?
Jul 20 '20 at 22:14 comment added Harper - Reinstate Monica Oh boy I think I see a huge mistake. I need you to unplug the Ginny and turn off every breaker in the panel. Including the main. Now I need you to set your meter to resistance and measure between the red and black screw on the back feed breaker this must be the only breaker that is on. Do you get zero ohms?
Jul 20 '20 at 21:36 history edited Ron CC BY-SA 4.0
added 332 characters in body
Jul 20 '20 at 21:28 comment added Ed Beal Do you mean the ground bond in the generator has been lifted to prevent a parallel current path! Lifted or not if the connections are correct it will not matter.
Jul 20 '20 at 21:20 answer Ed Beal timeline score: 3
Jul 20 '20 at 20:52 review First posts
Jul 20 '20 at 21:25
Jul 20 '20 at 20:51 history asked Ron CC BY-SA 4.0