Jul 20, 2020 at 14:53 | answer | added | Harper - Reinstate Monica | timeline score: 2 | |
Jul 20, 2020 at 14:28 | comment | added | Ed Beal | @jwh20 , Even in the 2020 code metallic water pipe is still allow as a grounding method 250.53.D, not allowed gas pipe aluminum and as outlined in 680.26.B,1 & 2 per 250.52.8.B | |
Jul 20, 2020 at 14:14 | answer | added | Ed Beal | timeline score: 1 | |
Jul 20, 2020 at 13:35 | comment | added | jwh20 | Water pipe grounding is no longer an acceptable practice because it doesn't provide a secure grounding point and, as you noted, the use of non-conductive pipes impacts that further. You should have a properly installed ground rod and bond the panel to that as required by your local code. I'm assuming you pulled a permit for the work you are doing, right? If not, it's time to get one. | |
Jul 20, 2020 at 13:34 | comment | added | George Anderson | The "grounding wire" going back to the transformer is your neutral conductor. What is the current grounding wire connected to? Is it a metal pipe supplying the water? But yes, these days code requires 2 ground rod at least 8' (?) apart and connected to your panel's ground bar (or neutral) if not a sub-panel and neutral is bonded to ground there. | |
Jul 20, 2020 at 13:28 | review | First posts | |||
Jul 20, 2020 at 13:45 | |||||
Jul 20, 2020 at 13:26 | history | asked | Andy | CC BY-SA 4.0 |