Jul 20, 2020 at 14:53 answer added Harper - Reinstate Monica timeline score: 2
Jul 20, 2020 at 14:28 comment added Ed Beal @jwh20 , Even in the 2020 code metallic water pipe is still allow as a grounding method 250.53.D, not allowed gas pipe aluminum and as outlined in 680.26.B,1 & 2 per 250.52.8.B
Jul 20, 2020 at 14:14 answer added Ed Beal timeline score: 1
Jul 20, 2020 at 13:35 comment added jwh20 Water pipe grounding is no longer an acceptable practice because it doesn't provide a secure grounding point and, as you noted, the use of non-conductive pipes impacts that further. You should have a properly installed ground rod and bond the panel to that as required by your local code. I'm assuming you pulled a permit for the work you are doing, right? If not, it's time to get one.
Jul 20, 2020 at 13:34 comment added George Anderson The "grounding wire" going back to the transformer is your neutral conductor. What is the current grounding wire connected to? Is it a metal pipe supplying the water? But yes, these days code requires 2 ground rod at least 8' (?) apart and connected to your panel's ground bar (or neutral) if not a sub-panel and neutral is bonded to ground there.
Jul 20, 2020 at 13:28 review First posts
Jul 20, 2020 at 13:45
Jul 20, 2020 at 13:26 history asked Andy CC BY-SA 4.0