when toggle format what by license comment
Jul 28, 2020 at 17:18 vote accept Stanwood
Jul 16, 2020 at 3:46 history edited Stanwood CC BY-SA 4.0
Added 2-disconnect idea
Jul 16, 2020 at 3:18 comment added Stanwood @ThreePhaseEel just added these in.
Jul 16, 2020 at 3:17 history edited Stanwood CC BY-SA 4.0
Added PNs
Jul 15, 2020 at 15:44 comment added ThreePhaseEel Can you provide us with make/model info for the new compressors then?
Jul 15, 2020 at 15:43 comment added Stanwood I can. But I’m replacing the compressor.
Jul 15, 2020 at 15:42 comment added ThreePhaseEel Can you post a photo of the existing compressor's nameplate please?
Jul 15, 2020 at 15:41 comment added Stanwood The HVAC installer has asked for 240VAC 40A and 20A circuits. Each with a fused disconnect. Does that make sense due to the 80% rule? I don’t follow why a fused disconnect is required if the circuit has an HACR breaker at the panel.
Jul 15, 2020 at 15:31 answer added Harper - Reinstate Monica timeline score: 1
Jul 14, 2020 at 21:17 answer added Ed Beal timeline score: 3
Jul 14, 2020 at 20:48 history edited Stanwood CC BY-SA 4.0
added image of existing disconnect
Jul 14, 2020 at 20:42 history asked Stanwood CC BY-SA 4.0