Jun 16, 2020 at 1:35 comment added Sylvain Cussonnier (E) Headroom The minimum headroom of working spaces about service equipment, switchboards, panelboards, or motor control centers shall be 2.0 m (6 1/ 2 ft). Where the electrical equipment exceeds 2.0 m (6 1/ 2 ft) in height, the minimum headroom shall not be less than the height of the equipment. Exception: In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (6 1/ 2 ft)
Jun 16, 2020 at 1:33 comment added Sylvain Cussonnier My crawlspace is around 4ft where the panel is, I thought it was possible because of this "110.26 (E) exception"
Jun 15, 2020 at 23:10 history edited Harper - Reinstate Monica CC BY-SA 4.0
added 395 characters in body
Jun 15, 2020 at 23:05 history answered Harper - Reinstate Monica CC BY-SA 4.0