Apr 26, 2020 at 2:53 comment added Clifford Eby Use of 10ga wire in a 50A circuit is a problem. Should be 8ga minimum.
Apr 26, 2020 at 2:52 comment added Clifford Eby The 15A breaker in a sub-panel as described works fine. I don't understand why you have to GFIC ground to a neutral. Keep it separate.
Apr 25, 2020 at 16:16 comment added mnvelocitypilot That's why I had the idea of a second ground rod.
Apr 25, 2020 at 16:16 comment added mnvelocitypilot So, in theory, I'm protected. BUT, to do this, I'd have to run the 120V GFCI outlet ground and neutral BOTH to the 240V neutral.... making a connection between neutral and ground outside of the main panel (dangerous and wrong). That
Apr 25, 2020 at 16:15 comment added mnvelocitypilot Thanks, Clifford - VERY helpful. I understand the issue with the potential ground loop created by two ground rods. What I was planning was to take one of the two 240 hot lines into a separate box with a 15 amp breaker, which then feeds a third box containing the 120V GFCI. The 10 gauge wire feeding the pool heater, which is protected by a 50A breaker. So, my thinking is/was, if the heater is on and drawing 40 amps, and I draw more than 10A via the 120V GFCI, I trip the 50A breaker. If the pool heater is off and I draw more than 15A from the GFCI outlet, I trip the 15A breaker.
Apr 25, 2020 at 16:03 history answered Clifford Eby CC BY-SA 4.0