TLDR: Replace every breaker in your panel with a BR type from Bryant, Cutler Hammer or Eaton, readily available most places that sell breakers. Nothing else should be in your panel - especially not a Challenger (unless you like fires)!
For the best answer ever on this subject, see here.
Green highlighting added. The breakers don't actually have that.
You must use UL-listed or UL-classified breakers
UL-listed means the manufacturer of the panel makes the breakers using their internal knowledge, and UL certified it as safe.
UL-Classified means a competitor reverse-engineered it. UL has torture-tested it and confirmed it safe.
Never stick random Brand X breakers in your panel. The bus stabs are different for patent reasons, and will arc and burn when heavily loaded. We call these "alien breakers".
Challenger is cursed...
Challenger acquired this line from Westinghouse (Tesla's friend in the War of the Currents). Because Because of the need for backwards compatibility, one cannot change a bus design. ButBut it's a good bus design. Unfortunately Challenger hopped on the FPE/Zinsco crazytrain and made some very bad breakers for that good bus. That is why Challenger is on the "Kill it with fire before it kills you with fire"same "remove it" list as FPE/Zinsco, but only insofar as the breakers, not the panel.
... but Challenger is blessed.
This industry runs on mergers and acquisitions. Challenger/Westinghouse wound up in the hands of Bryant bought Challenger (for a song, no doubt, lol) andwho promptly fixed the breaker problem. They changed its name to BR, so they could outlaw use of the defective Challenger Type C breakers. (The buses remain the same). As for BR breakers, they cross-listed those Type C, since of course they fit Challenger. This gives Challenger panel owners a super easy upgrade path; simply swap out the vile Type C for Type BR/C for about $5/circuit. It also continues to support Westinghouse panels.
To be clear: BR/C isn't "UL-classified" for your panel. It is "UL Listed" for your panel. And your only legal choice.
BRyant sold their breaker division togot folded into Cutler Hammer, who sold it togot folded into Eaton. The buses are still the same to maintain backwards compatibility and because Westinghouse'sthe original bus is perfectly fine.
You must change every breaker in the panel to BR type
Since the Challenger breakers are dangerous and Westinghouse breakers are really old, every breaker in your panel needs to be a Type BR/Type C from Bryant, Cutler Hammer or Eaton. If it's not, change it now.
Also, where your breaker has failed, look closely at the bus stabs under the breaker. Challenger never had a bus-stab problem, but lots of people don't know about the BR/C thing. If some fool stuck an, so they run out and grab any "alien breaker" in there like a Square D HOMeline or GE or Murray, that. Those could have burned up the bus. A burned bus is unusable; that space is permanently dead. Search the panel for any other alien breakers and get rid of em.
An alien breaker can be a sleeping monster; most circuits aren't loaded very hard (until they are, and that's when it fries).