Skip to main content
16 events
when toggle format what by license comment
Jan 27, 2020 at 9:04 history edited Harper - Reinstate Monica CC BY-SA 4.0
added 224 characters in body
Jan 27, 2020 at 9:03 comment added Harper - Reinstate Monica @ThreePhaseEel yeah, it's pretty easy. By the by, here's a comparison of those two cables crammed into 3/4 Sched 80 PVC (no way!!!) versus 29% conduit fill in 1-1/4" EMT, which is legal. Barely. It's at 29% fill (counting "treat as a circular wire"), and it's almost at the 30% limit for 2 wires. There isn't even space for a bare ground wire. (well actually there is, since a ground wire would be a third wire, raising the fill to 40%).
Jan 27, 2020 at 8:57 history edited Harper - Reinstate Monica CC BY-SA 4.0
added 224 characters in body
Jan 27, 2020 at 7:47 history edited Harper - Reinstate Monica CC BY-SA 4.0
deleted 1 character in body
Jan 27, 2020 at 7:41 history edited Harper - Reinstate Monica CC BY-SA 4.0
deleted 1 character in body
Jan 27, 2020 at 3:33 comment added ThreePhaseEel Also: awesome pics re: the situation with cables in conduit vs individual wires
Jan 27, 2020 at 2:53 comment added ThreePhaseEel One other thing: Schedule 80 PVC (worst case for fill) won't fit a 70A feeder (as that requires an 8AWG EGC, which overfills the conduit slightly) -- that isn't an issue for Schedule 40 PVC or EMT though
Jan 27, 2020 at 2:47 comment added ThreePhaseEel Ah! Good catch, thanks!
Jan 27, 2020 at 2:27 comment added Harper - Reinstate Monica @ThreePhaseEel you mean wall thickness x 2 right?
Jan 27, 2020 at 2:15 comment added ThreePhaseEel Try adding the "minimum average ID" to the "minimum wall thickness" on that table
Jan 27, 2020 at 2:10 comment added Harper - Reinstate Monica @ThreePhaseEel Yeah, I checked that. 15/16" is 0.938", which is dead-nuts halfway between sizes, 0.100" from either one.
Jan 27, 2020 at 2:00 comment added ThreePhaseEel I'm suspecting it's off-nominal (but still within spec) PVC (either S40 or S80) -- the specs I've seen for PVC conduit allow for outside diameters well under 15/16"
Jan 27, 2020 at 2:00 history edited Harper - Reinstate Monica CC BY-SA 4.0
added 208 characters in body
Jan 27, 2020 at 1:49 comment added Harper - Reinstate Monica @ThreePhaseEel I thought that. But then, OP reports 15/16" OD (fairly specific). I searched both plastic and RMC/IMC conduit; none had diameters anywhere near that (under 7/8" or over 1"). That's not surprising since threaded or glued pipe must have a consistent OD. EMT, which is 0.922", is almost precisely 15/16".
Jan 27, 2020 at 1:44 comment added ThreePhaseEel The OP stated their conduit was plastic, not metal
Jan 27, 2020 at 1:33 history answered Harper - Reinstate Monica CC BY-SA 4.0