Aug 20, 2019 at 2:03 comment added Harper - Reinstate Monica Note the abstract, which discusses branch circuits. This is feeder. Yes, that is outlawed for all interior wiring. Now you must use the AA-8000 alloy, and nobody's going to use it for branch circuits if they like to ever sell their house, but it's fine for feeder.
Aug 20, 2019 at 1:46 comment added ThreePhaseEel @Flinch -- most AHJs are fine with aluminum these days, given that in-building wiring types are generally required to use AA-8000 series alloys (vs. the finicky AA-1350/EC that got aluminum its bad rap) by NEC 310.106(B). Furthermore, the 2017 NEC took a major step towards addressing the true cause of termination burnouts by adding the 110.14(D) torquing requirement for all places where termination torques are marked on equipment labels.
Aug 20, 2019 at 1:44 comment added Pete Donaldson Harper: Why schedule 80 vs 40. Flinch. I can see not using Aluminum for receptacles etc. I would guess improvements have been made in technique and wiring since 1974. Seems that almost all of the opinions I have reviewed recommend Aluminum on longer sub panel runs. Aluminum is what is the Panel coming from the Meter and feeding all of my HVAC equipment.
Aug 20, 2019 at 0:49 comment added Flinch Right you are. I missed that on account of personal prejudice over the years - I never run aluminum for anything. Ever. Most state building codes have done away with it I think [except for temporary construction], and it can be a problem for your homeowners insurance regarding coverage. Here's a study that's more in depth [note the 1969 UL/NEMA survey on page 25]: nvlpubs.nist.gov/nistpubs/Legacy/IR/nbsir75-677.pdf
Aug 20, 2019 at 0:10 comment added Harper - Reinstate Monica I think you mean 1 AWG aluminum, alternate 0 AWG. Your numbers would be fine for copper but he wants Al.
Aug 20, 2019 at 0:05 history answered Flinch CC BY-SA 4.0