Jun 13, 2019 at 14:04 | comment | added | JPhi1618 | Yea, don't worry about the copper plates, but find out where that lone, large neutral wire goes that exits out of the bottom of the panel. Kinda odd - might go to the grounding rod? | |
Jun 13, 2019 at 1:06 | comment | added | Harper - Reinstate Monica | Puff, you're replacing the panel??? Who cares about those copper things, then? They stay with the Zinsco panel. You certainly won't be moving them into the new panel... unless you somehow got a NOS Zinsco panel... | |
Jun 13, 2019 at 1:02 | comment | added | cadobe | Good point. Moving on those red breakers. The thing is I need to replace the panel (see this question: diy.stackexchange.com/questions/167133/…) meanwhile cleaning the mess and make my understandings | |
Jun 13, 2019 at 0:55 | comment | added | Harper - Reinstate Monica | Are the copper plates a problem for you? I mean all I would say is I would pull them out and wrap them good-n-plenty with electrical tape, or paint them with Glyptal, but that's all I would do. You are strettttttching the very last possible life out of a very old, obsolete and dangerous panel that should have been replaced in the 90s, part and parcel of that is that kind of tacky compromise. | |
Jun 13, 2019 at 0:54 | comment | added | Harper - Reinstate Monica | Notice the two red breakers in the Rule of Six area have nothing on one side. How about moving the two #12 wires that are in the sub panel on red breakers, to those terminals? | |
Jun 13, 2019 at 0:51 | comment | added | Harper - Reinstate Monica | @cadobe You can't. First, that would put more than 6 throws in the Rule of Six area, and second, those breakers are not bussed that way. They won't take their power from that bus. | |
Jun 13, 2019 at 0:49 | history | edited | Harper - Reinstate Monica | CC BY-SA 4.0 |
added 117 characters in body
|
Jun 13, 2019 at 0:48 | comment | added | cadobe | That means, if I want to have everything below the white breakers working without the copper plates I have to move them above the white ones? | |
Jun 13, 2019 at 0:42 | history | answered | Harper - Reinstate Monica | CC BY-SA 4.0 |