Yes, the critical issue is voltage drop due to resistance, which is both a function of conductor size and plug connections. One 100' #12 cord is better than two 50' #12 cords, for example, because there will be fewer contact connections.

I wouldn't hesitate to use your saw on a 100' #12 or #10 cord, assuming that you're not already at the end of a very long outlet circuit as well. You can check voltage across the plug contacts to make sure you're within about 5% of nominal (120v). As brhans pointed out in the comments, this would need to be done while the tool is under load.

Yes, the critical issue is voltage drop due to resistance, which is both a function of conductor size and plug connections. One 100' #12 cord is better than two 50' #12 cords, for example, because there will be fewer contact connections.

I wouldn't hesitate to use your saw on a 100' #12 or #10 cord, assuming that you're not already at the end of a very long outlet circuit as well. You can check voltage across the plug contacts to make sure you're within about 5% of nominal (120v).

Yes, the critical issue is voltage drop due to resistance, which is both a function of conductor size and plug connections. One 100' #12 cord is better than two 50' #12 cords, for example, because there will be fewer contact connections.

I wouldn't hesitate to use your saw on a 100' #12 or #10 cord, assuming that you're not already at the end of a very long outlet circuit as well. You can check voltage across the plug contacts to make sure you're within about 5% of nominal (120v). As brhans pointed out in the comments, this would need to be done while the tool is under load.