If my picture messed up during resizing - it looks like a jumper wire between the two screws on the hot side of this outlet.
2 Answers
Someone broke the fin off, then had breaker's remorse
A factory-new duplex receptacle has a copper "fin" connecting the two screws on each side -- breaking this fin off on the hot (brass) side is done when you want a half-switched receptacle outlet, for instance. It appears somebody broke the fin off at one point, then either the same person or a different person had regrets about the broken fin and replaced it with a jumper wire. So, leave the fin on your new receptacle, and all will be well.
It looks like the outlet was used at one time with that factory installed jumper removed. That would allow you to have two circuits serve each outlet on there. This is often done when you have lights that plug in, you would wire a switch to one outlet for the light, and the other one would still be usable for other things.
I don't think it's legal to put a jumper back in there, typically you can only have one wire per screw terminal.@Makyen pointed out that in this case, the jumper is the only wire in the screw terminal, and the actual circuit wire goes into the push in terminal at the back, so that part of my answer does not apply here.
-
Thanks - I'm replacing the receptacle entirely. So should I just remove that and otherwise wire normally?– beeCommented Nov 10, 2018 at 22:50
-
Yes. If you look at your new receptacle, you'll notice the factory installed jumper. Commented Nov 10, 2018 at 23:48
-
7@PhilippNagel In this instance, there is only one wire per screw terminal. The incoming hot wire appears to be using the back-stab connection at the rear of the outlet.– MakyenCommented Nov 11, 2018 at 0:47
-
1Ah @Makyen I missed that in the photo. Thanks for pointing it out! Commented Nov 11, 2018 at 2:09
-
2Backstabbing is the worst thing to do. I've had to pull and rewire every device in houses wired with backstabs. Commented Nov 11, 2018 at 14:51