revised Bar sink drain/vent
Updated answer due to new information
Apr
1
comment Bar sink drain/vent
The link to the first picture is not working.
Mar
31
comment Bar sink drain/vent
The vent needs to stay vertical until it passes the heigh of the sink's flood level rim (the level of the sink's rim where water would overflow if plugged). After that height, it can be run horizontally to the vent stack. The connection to the vent stack should also be above any fixture's flood level rim. (The gray mono-spaced text is done by formatting the text as code, I've updated your post's formatting.)
Mar
31
revised Bar sink drain/vent
formatting
Mar
31
comment Bar sink drain/vent
That would depend. Where I’m from, if the wet vent is 2”, it can handle a total of 3 fixture units of load in addition to the load of the toilet. A bathtub and a sink are 1-1/2 fixture units each, so in this case it would work (as long as the bathtub pipe is 1-1/2"). However, the wet vent will not act as the vent for the sink so you would still require a separate vent for the sink regardless on how the drain is connected.
Mar
31
answered Bar sink drain/vent
Mar
31
awarded  Custodian
Mar
31
reviewed Approve How do you access the Rainsoft water softener “advanced” settings, such as hardness?
Dec
24
comment What pipe/adapter do I need to make this sink connect to this P trap?
To clarify: you do not connect directly to the ~2" outlet on the bottom of the sink. You would instal a drain assembly the same way as you would on a porcelain sink. The nut (part RP6140 in @Tester's image) would but-up to the underside of the ~2" sink outlet. Tightening it will compress the flange to the inside of the sink. Your p-trap is most likely 1-1/4" and a 1-1/4" drain assembly would fit though the sink's outlet.
Nov
19
answered How to check issue with Gas fire place?
Oct
20
awarded  Nice Answer
Aug
29
comment Why would there be hot water through the cold water side?
What was the water pressure before the booster pump? And after? Also, are there any check valves installed on the cold feeding the hot water heaters?
Aug
28
comment Air handler condensation draining problem
@Tester101, The trap is not to prevent sewer gas in this application. It's purpose is to maintain separation between zones of different air pressure while allowing the condensate to drain.
Aug
27
answered Cold water entering hot water circuit?
Aug
27
comment What type of copper pipe do I need for a typical LP gas range?
Also note that if you do replace the copper tubbing with copper tubing: while they sell compression fittings that will fit the copper tubing, typically compression fittings are not allowed on gas. You should confirm with your local code, but it will most likely require flared or solder connections.
Aug
27
comment What type of copper pipe do I need for a typical LP gas range?
I would be very surprised if copper was not approved for gas. There are issues with the type of fittings used when using copper for gas installations, such as compression fittings are typically not allowed (must use solder or flared).
Aug
27
answered Is this a refrigerator water hookup?
Aug
27
comment Air handler condensation draining problem
Your best bet is to look up your unit on the manufactures website and find the installation manual. It should include information on how to size the p-trap to account for the unit's operational pressures. If they don't explicitly detail the p-trap, you should be able to get the operational pressure and use the article I linked to to get the dimensions.
Aug
27
comment Air handler condensation draining problem
If the compartment has a negative pressure, you should have a p-trap.
Aug
27
answered Air handler condensation draining problem