4

According to the instructions found here, you'll have to replace the other switch with a Retractive Press Switch when using a dimmer. Important notes - for two way and multi - way installation Read General Installation Safety Instructions before starting work. Any existing 2 Way or Intermediate switches MUST be replaced with Retractive Press ...


3

There are half a dozen ways one could do this, but I would do it this way Purchase 2 Lutron RF Maestros. ( The RF part is important, as they sell none RF Maestros too) ( for non dimming use MRF2-6ANS ) One Pico wireless switch One Pico switch plate adapter One 2 gang decor plate Change both switches to the RF Maestro and put the Pico next to the ...


3

That looks like a doorbell transformer. Those smaller wires should lead to your doorbell chime unit (assuming you have a doorbell). The junction box is there simply to provide power to the doorbell transformer. From the picture it looks like you have 12/3 and 14/2 in that box, but it is difficult to tell. How confident are you the larger wires are larger ...


3

As suggested by Speedy Petey, I poked around further into the back of the wall box and it turns out there was in fact, some white wire. This gave me what I needed to match the diagrams on the Insteon sheet, the unit is now connected as diagrammed and functioning as intended.


2

On your switch that you bought the Black is the Line (Power coming in), the Red is the Load (Power to the Light), the White (which you do not have) is the Neutral and the bare copper wire is the ground. Insteon used to sale a 2-wire kit but the product is now unavailable. You are going to need to get neutral down to light switch(12/3 Romex) or look at ...


1

Most likely, the hot wire is coming first to the other 3-way switch. From there, power comes on one of the two travelers to the 3-way you're working with. You've probably connected your new switch to one of the travelers. I'd bet if you switch the other 3-way, the light will come on and off together. Without the hot coming to this 3-way, you cannot have ...


1

From your description, I can only guess what your wiring is: If my guess is correct, you'd need to wire it like this: Note: The black/white wire order in the Switch Box has been swapped in the 2nd diagram! (so the wires wouldn't overlap) You will need to confirm the wiring yourself using a multimeter.


1

First turn off the circuit at the breaker panel. A good practice is to confirm that there is no power on any cables in boxes you are working on using a non-contact tester. If the switch only has one 2 conductor cable in its box, it is a switch loop. That means the power from the mains comes to the switched fixture box (in your case, the outlet) and only the ...


1

@AndyMcKenna No, the way you have the switches wired will not work correctly. If you look at your new switches there should have 3 terminal screws. There should be two copper looking screw(traveler wires), setting across from one another, and one dark screw(power in and power to the fixture) at the bottom of the switch by itself. Warning: You'll be ...


1

PROBLEM RESOLVED! #5 was a switch connection from the timer. #1 was porch lights. #2 was main feed. #3 was living room outlets and #4 was no longer used


1

Updated solution per comment: The fire alarm should not be connected to a switch at all. It's likely that it is connected to the same switch as the light but with the wires reversed. The solution would be to remove the fire alarm black & white wires from the switch and splice them in the box to the cable that feeds the switch, but before it "hits" the ...


1

This would be fine if you mount the switch in an electrical box in the wall and use it, for example, to switch the receptacle (or just half of the receptacle) that your surge suppressor or battery unit is plugged into. For instance, you could us an "old work" box to put the switch in the wall above the desk, and fish NM cable to/from the box with the ...


1

Easy. Cap off the red at both locations. The remaining black wires at the wall will connect to a standard single pole switch, and the remaining wires in the ceiling will connect to the receiver as directed by the manufactures instructions.