Tag Info

Hot answers tagged

49

More than you've ever wanted to know about the C wire: Lets start by explaining what the C wire is, and why it's needed. Ye olde thermostat In the olden days thermostats were simple switch devices, that used Mercury Switches to complete the circuit and turn on the heat/AC. Mercury switches were commonly used in bimetal thermostats. The weight of the ...


25

I think you will just waste a lot of water compared to the cooling effect that you get. A better way to cool the roof is to change its color. A roof with a clean, smooth bright white surface can reflect about 85% of incident sunlight and emit thermal radiation with 90% efficiency. This surface will be only 9°F warmer than the outside air on a typical ...


22

I went though a similar debate last year and ended up getting a whole house humidifier. I never remember reading that you should be able to get the humidity level to normal levels though normal means (shower, cooking, etc). In a big house, that is most likely not possible. Do you have a humidistat now, or does your stand alone unit give you a reading? I ...


15

In the winter it is 30 to 40 percent in cold climates. During the summer, indoor humidity levels should be kept below about 65 percent to minimize the potential for mold growth and below about 50 percent to minimize dust mites. See this article for some more great information on humidity levels: Keep Your Home Healthy


14

Looking in 2011 National Electric Code Changes of Interest, they reference NFPA 90A-2009 : Section 4.3.4 of NFPA 90A-2009 states that “Wiring shall not be installed in air ducts” unless it is “directly associated with the air distribution system and does not exceed 1.22m (4 ft).” I don't have access to the full code, but just in the notes on the ...


14

I assume you are in a cold climate, like Minnesota (where I am). I will address your question in three parts; the first two have to do with the humidifier. The "winter" setting on the duct in your photo: It appears from the photo that the duct in question goes from your humidifier around to the return (intake) side of your furnace's ducting. This needs ...


12

You may be looking at the problem backwards, the freezing lines could be a symptom of the problem not the cause. Start by looking for blockages in the system that would cause lower air flow / heat exchange. Dirty filters. Clogged ducts. Closed dampers. Closed/Blocked vent covers. Dirty coils. Basically if the system cannot exchange the heat/cold, it ...


12

The logic involved is much more complex. Right now the logic is simple: if AC Mode and it's too hot, turn on AC, else turn off AC if Furnace mode and its too cold turn on furnace, else turn off furnace But the determination of when to switch between heating and cooling modes is much more complex - otherwise the ac would kick on, and it would get too ...


12

Sounds like a classic compromised leg of your main service. This problem could be anywhere from the connections at the utility transformer on the pole, to the connection taps on the side of the house, to the meter pan, to the main breaker. IMO this is NOT something for a DIY to troubleshoot since you would need to be testing live unfused wires in places ...


11

Yes, placing registers (or other heat sources such as radiators) near exterior windows and doors is the usual practice. This is done in order to combat cold drafts and ensure a more even temperature throughout the room. Here's a Q&A on the subject from Ask This Old House: Window glass is the coldest part of a wall. When warm room air hits it, the ...


11

After reviewing the spec sheet for the unit i have found that the LX series has a variable speed blower that will allow the unit to operate under low ambient conditions. Is specifies the system can operate down to 20 degrees. Anything below this and the system will not operate. If you do not have the LX unit and do have the standard, the. The unit is not ...


10

You'll want to check out the ENERGY STAR Air Conditioning Sizing Calculator.


10

They do make thermostat controlled vent covers, this particular one is ~$60. I'm not sure how difficult it is to install one of these (as I've never done it myself), but it sounds like this is exactly the type of thing you are looking for. This is not a recommendation for this product, simply an example to show that they do exist.


10

National Electrical Code 2008 300.22 Wiring in Ducts, Plenums, and Other Air-Handling Spaces. (B) Ducts or Plenums Used for Environmental Air. Only wiring methods consisting of Type MI cable, Type MC cable employing a smooth or corrugated impervious metal sheath without an overall nonmetallic covering, electrical metallic tubing, flexible ...


10

I wouldn't do it. The next poor sod (who may be you) trying to fix something (or perhaps changing the system!) is expecting to find properly colored #18 AWG wire. Instead they'll find #24 wire in all these weird (to them) colors. You're saving yourself some money now, and making someone else's life difficult down the line. And of course, if you or someone ...


10

The technology is relatively young, and not as well known to consumers as traditional heating and cooling methods. The upfront costs of a geothermal system are also higher, and there are fewer companies around with the knowledge and tools to install the systems. In the US most homes are not built by the home owners, they are built by development companies ...


10

That pipe looks like an air intake. All "direct vent" style appliances (high efficiency on-demand water heater, gas fireplace, etc.) have an isolated air intake and it is common to have it suck in air from outside the building so as not to force air infiltration through doors, windows, etc. Indeed, that is ugly. Our fireplace and tankless water heater ...


10

It helps for sure. There have been a ton of studies done on this and I have read at least 10-11. At one point in time I was going into a partnership for a "greening" business. Your variance is somewhere between 1-15%. There are a ton of variables. Here is an OK study I read a few weeks ago from FSEC. I personally don't like this study because they ...


9

I seems to me that waxing the outside of the AC unit is only going to protect cosmetic appeal. If you're interested in keeping the unit looking nice from the outside, then it could help. Otherwise, I wouldn't put in the effort.


9

I live in south texas, last week we had a terrible heat wave, temperatures outside where in the 110F-115F range, I installed a wireless thermometer on the attic and it read 130F on the hottest days. Ac would not cut off when set at 77. Went to home depot, got a set of 3 sprinklers that you can connect in series, I had an extra 24v solenoid water valve around ...


9

A thermostat basically just energizes the individual circuits (G (fan), W (heat), Y(cool) ) which in turn (via the furnace controller) powers a relay which provides line voltage to the actual units (like the fan or A/C. In the case of heat, it instructs your furnace to open the valve supplying gas). R (or Rh and Rc) provides the 24VAC power. To turn on ...


9

It's not the efficiency which you get -- it's less dust in the air. Less dust equals better health in the long run. Lots of dust in the ducts is an indication of a bad air filter and/or leaks around the filter or in places where ducts join/turn. I'd look for that as well.


9

Necessary? No. More efficient? Yes. When the HVAC is centrally located the warmer/cooler air has less overall distance to travel to cover the entire house, as it's radiating out from the center. If you have noticed that one side of your house is less comfortable than the other, it may be worth the relocation. If the house is generally comfortable year ...


9

A properly functioning and properly sized central air conditioning unit should be able to maintain the temperature of your house at any reasonable temperature you select. The amount of cooling available is related to the size of the system, insulation in the house, and finally outside air temperature. From your description I would guess either you don't ...


8

Check your unit's warranty. The heat exchangers on some units are warranteed for 20 years or longer. You may be able to get at least some money from the manufacturer, or a credit toward a new unit of the same brand. They may also cover all or part of the installation labor. Find out whether there are any federal or state tax incentives that could help. A ...


8

High efficiency furnaces will make condensate. They run the air back through the hot exhaust to get more heat out. This also cools your exhaust enough to use PVC - that's what your upper line is. In the process of cooling the exhaust, you might get some condensation. Typically that's collected in a little sump tank. When the sump reaches a certain level, a ...


8

The device you linked to will work. You are essentially converting to a SPST "thermostat" from your current DPST thermostat. Some people feel a SPST thermostat is dangerous because the heating device is always connected to a hot leg of the power mains. Both legs are disconnected with a DPST device. Yet this SPST practice is common and acceptable in many ...


8

There are various degrees of a "zoned" HVAC system. A simple zoned system will include motorized dampers in the ducts to direct air where it is needed. e.g. If one room is too cold, but the other ones are fine, the system will shut the dampers to the other rooms, and then fire up the heater so just the one room is heated. More sophisticated zoning systems ...


8

For the ducts, the setting indicates where you should set the switch based on the season. If your house has separate air return ducts on different floors or even multiple ducts on the same floor, changing the setting changes which ducts pull air from the house, allowing lower ducts to suck cold air out in the winter and higher ducts to suck hot air out in ...