You think you've found all the nails-through-wires, but there's one more. I once had a friend who's garage light switches suddenly started operating different lights, and I traced it to a 16p nail that a roofer had put through two separate runs of wire, one of which was a three-way switch send, and the other a regular single send. The nail shorted one leg ...


3

Turn off all the breakers, try them one at a time and see when the voltage returns, this should help to locate the problem area. Once you have the area found, turn on all the breakers, except the breaker to that area, and check it again. Now with the problem breaker/breakers off, go through the devices and check if any have a bad wire. I would start with ...


0

Thanks guys, I spoke with an experienced electrician who validated my concerns and gave me two options after I explained to him that I am not concerned about a three way switch. Replace the 20A breaker and goofy three way switch wiring in the house with a 40 or 60A double pole breaker. Continue to use the 100A three conductor (SEC cable). Install a ...


1

The sub panel will need the ground to be separated from the neutral. The only place they are joined is inside the main breaker panel. This prevents open neutrals between the main and sub panel from sending current over the ground, and possibly electrocuting someone if a better path to ground can be found. For the 3 way switch, I'm guessing you need to trace ...


7

According to National Electrical Code, the pipe has to be bonded. However, it can be bonded using the grounding conductor serving the equipment that uses the gas. ...The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means... As for lightning strikes, the gas company is ...


0

My power company requires it be in non-metallic conduit. http://www.cityofames.org/modules/showdocument.aspx?documentid=3535


1

Follow the manufacturer's instructions for wiring the device. If the instructions say make a ground connection, then make it. For argument's sake, that ground could very well be for nothing more than grounding the switch (so it wouldn't necessarily be a pole). However, it is likely that this device is indeed passing some current to ground. Below is a ...