1

Code may vary where you live Yes. You are going to create a "Shared Neutral" circuit. This isn't difficult or dangerous, but you should do some labeling in the panel and the box itself. First, it looks like the receptacle is a 30A/220V grounded receptacle (the wire itself may also be 30A -typical for an electric dryer- but that doesn't matter since you ...


1

Sounds to me like an open neutral. This will give you a reading of voltage (to ground or with a pen tester) but the circuit will not work. You need to check the connections at every device on the circuit.


4

The amp rating of the receptacle and circuit do not depend on whether the receptacle is a GFCI or not: If you have a 15 amp circuit, you must have 15 amp receptacles If you have a 20 amp circuit, you can either have 20 amp receptacles, or 15 amp receptacles if there is more than one (e.g. a duplex receptacle). It's not unusual to have a 20 amp GFCI in a ...


4

1) You can have a GFI receptacle on either a 15 or 20A circuit. Keep in mind, areas like kitchens, bathrooms, laundry, etc, typically require 20A circuits for receptacles. For areas like outside and garages 20A circuits are always a good idea. 2) Either. You can have a GFI receptacle and feed everything downstream of it off the LOAD terminals protecting ...


1

Steven - I am also in Vancouver, and just installed a new kitchen with permits and inspections. Yes, the gas range and hood can be on the same 15A circuit, as mine are. Just be sure that the oven is also gas, and does not have any electric broiler or electric self-clean. If the rating is under 12A you are fine. If you are splicing into an existing 15A ...