They DO pass current through the switch and light at all times - just a few mA. The indicator is wired in parallel to the switch contacts. For most types of bulbs its not enough for the light to turn on. However with modern LED light bulbs these types of switches (as well as dimmers, and home automation switches) that dont use the neutral can cause the ...


3

It sounds like you have a bad connection or a broken wire somewhere upstream of your main breaker. Assuming that the power company's test were valid, then the problem would be the wire between your main breaker and the power meter. Other possibilities are that your main breaker is bad, or that the meter, meter box, or something upstream of that is broken. ...


2

The shaking probably shook a wire loose besides causing a leak, or the leak flooded over a set of wires and shorted the wire to the casing. The GFCI did it's job by detecting the short to ground and shutting down the power. trying to reconnect with the fault in place will then cause the GFCI to trip again. The dryer is protected by the same GFCI so when it ...


1

The dimmer is blown, trying turning off the breaker and connecting the line and load for the chandelier(bypass the dimmer), and see what happens when you turn on the breaker. Most dimmer manufacturers recommend using a toggle switch to test new light fixtures, that way if there's a short you don't kill a good dimmer.