7

REPLACE THIS PANEL NOW Your panel almost certainly is suffering from breaker-to-busbar contact damage, rendering it a ticking incendiary device. See this answer for the gory details on just what is wrong with FPE's "breakers". If you post a picture of your panel (dead front off), I can determine if you can have your electrician install one of the Eaton ...


6

i am not an electrician but I do know federal pacific went out of business years ago after it was found that their boxes were responsible for a number of fires. Change the entire panel just to be safe. keeping the federal pacific panel is asking for a trouble.


3

Bottom line is NO, you definitely cannot do what you propose. You CANNOT parallel a circuit like this of this size. It is expressly forbidden in the NEC, and could very well be a safety hazard. If the appliance takes two separate circuits like your old one that is a different story. Do you know what size and type of wire is feeding the old 30A circuits? ...


3

The National Electrical Code defines a Multi-wire branch circuit as follows. Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or ...


3

Aside from being a code violation of outrageous proportions, if this is 120VAC you would have the delightful condition that the light sockets were always hot/live - this can make changing a lightbulb into a shocking experience, and under the right conditions, also your last. You may also get some interesting magnetic effects from the loop wiring. Don't do ...


2

Do not just install a 2 pole 50 amp Breaker. First your wire would need to be rated for the correct breaker. Second if the oven is rated at FLA (Full Load Amp) not to exceed 40 amps and there was a fault, the 50 amp breaker may not trip and could start a fire or kill someone. If you can wait look at Amazon, one quick search and there it was. Also look at a ...


2

If there's no current to the fixture or switch, then the fault is upstream. The fact that it was flickering indicates a failing connection, possibly arcing somewhere, which can be a fire hazard. You should check all the junctions on this circuit from the switch back to the breaker until you locate one with a good hot, neutral, and ground connection. And then ...


2

You have a FPE panel, so why are you trying to put breakers in it? Just replace the entire panel, as the panel is telling you to...the fact you can't stick a breaker in easily should be a gigantic red flag that something is badly broken inside and you shouldn't bother trying to repair it!


1

What is a Multi-wire Branch Circuit? A multi-wire branch circuit is two or more circuits that is served by a a set of hot wires connected to different phases (all with the same voltage between them) and a common neutral wire (all of the hots also have the same voltage with respect to the neutral). This arrangement saves a bit on wire and can also save on ...


1

Maybe I'm answering too soon (hopefully you'll post a diagram and/or pictures). But offhand and assuming you're using 120V AC power, this doesn't sound so good. Yes, there's a fair chance that you could make it function, but probably not really in compliance with the rules. It sounds like at best you're switching on the neutrals, but it's hard to tell ...