Tag Info

Hot answers tagged

7

Okay, so I think I figured out the reason, and I learned a lot about HVAC in the process. The answer is that a ceiling fan is moving air at basically zero "static pressure." Static pressure in an HVAC context means the amount of resistance that the air has to moving. In a free environment, that's zero, or close to it, but in a tightly restricted system of ...


5

After a bit of research, (translated: "mad google skills") I found an article claiming that lowering the blower speed may increase efficiency. I'm not completely convinced on this, since the claim is made by a company that sells variable speed blowers for retrofitting HVAC systems. I would think adjusting the heating element would save more energy than ...


5

This may be as simple as the "start" or "run" capacitor going south (because the motor starts but dies afterwards, I suspect that the run capacitor is blown). If you are comfortable digging around in the control box for the furnace, then you should be able to find 1 or 2 large-ish capacitors. If you have a multimeter, you can test them against the specs ...


4

Sounds like your blower may be done but I am not really sure. One thing to try is to call your Gas or Electric company and see if you have a service plan. Some utility companies include a service plan charge on your monthly bill (and you might not even know about it) and it includes 24 hour service.


4

Are you looking for something smaller than this? Porter Cable Pancake Air Compressor To get any kind of are pressure / volume, you need a compressor of a decent size. Those little mini compressors can inflate something, but it takes a long time and they don't have the volume of air necessary to blow dust.


4

If the furnace manufacturer supplies different burners for that unit you may be risking premature failure. The heat exchanger can be overheated and burned out if the blower does not remove enough heat. Proper duct sizing can resolve the issue you are having. Sometimes you have to add more ducts to achieve the proper pressure and velocity.


4

Some motors have a start up noise, and is normal for that type of motor. My table saw does this. Starts out a loud 60 Hz hum which quickly increases in frequency as the motor spins up, then gets inaudible or washed out by rushing air when full speed is reached. Motors that do this are not really appropriate for residential blowers. It also possible it's not ...


4

I would suggest using a small shopvac instead of an air compressor, for several reasons. Air from compressors contains moisture which can harm electronics. If you want anything more than a few seconds of air, you'll need a compressor with a high CFM output or a large tank. This means more money than you're willing to spend. I've got this 1 gal. compressor, ...


3

Just because the furnace fan is rated at 3/4 or more horsepower, does not mean that it is actually running at that power level. To clarify this, consider the extreme with an electric motor with nothing connected (just a shaft sticking out) spinning at full speed: it uses almost no power: perhaps as little as 3 watts, even though its ratings plate says 700 ...


3

Most furnaces use a preset, adjustable, time delay circuit to control the start of the blower motor. Some higher end models may use a temperature sensor to determine when the blower should come on, but this is a less common setup. It's possible that something in the furnace is broken and/or configured incorrectly, but it's more likely that the thermostat has ...


3

Squirrel cage blowers make great fans. Black is ground, white-negative and red-positive. Looks like blue, white and red coming from the motor. Read the info on the motor, it should have split capacitor in it, may have to change the wiring from 220 to 110. Looks like a 1/4-1/5 horse. Ask a local HVAC guy, feed his ego and be rewarded. If its a 110 just throw ...


3

The blower very likely does spin at different speeds when heating vs. cooling. This is not uncommon at all. In heating mode they typically are on a low speed, while in cooling or fan mode they are typically on high speed. As such, it could certainly be the case that there is some imbalance in your blower that excites a harmonic frequency of your furnace at ...


3

You are going to need something with a storage tank. The little "inflater" type compressors basically use the tire, ball, etc. as the storage tank. Because of this, they are not going to be able to blow air with any force. If you're just looking to blow dust from your keyboard, why not use compressed gas in a can? don't try to fill your tires with ...


2

Empirical Engineering Answers: Yes: you will save electricity costs by running your blower on low. No: you will not save on gas/oil costs by running your blower on low. Because the slower air velocity over the heat element is transferring fewer BTU units into the circulated air and they simply go up the exhaust pipe. The NET difference of the above two ...


2

I would contact the manufacturer of the fireplace; either by phone or on the web, they should have a blower designed for your fireplace. They may also provide instructions on hooking it up, or offer installation as a service.


2

This could be a bad draft inducer motor. This is a little motor that runs for a short while whenever your thermostat calls for heat and the furnace is in its initial firing + warmup stage. Our furnace failed this component (when it was only around 2yrs old), and the entire house would know when the furnace started running. Vibrations around the equipment ...


1

The blower motor - or squirrel cage like you call it-, is not the only moving part in the furnace; there is another motor which only runs when your A/C system is blowing hot air, its purpose is to expel the combustion gases produced by the burning fuel, usually natural gas. It is commonly called 'Exhaust Fan" . This could be what is causing the ...


1

Turns out someone decided to play with the dip switch on the back of the thermostat and set it to electric heat. Switching it back to gas heat fixed the problem. Luckily it was just a simple solution. :) Thank you for your help.