The installation of wire and/or electrical devices, to allow the transmission of electricity from one point to another.

learn more… | top users | synonyms

8
votes
4answers
212k views

What wire gauge do I need for a 100 Amp subpanel at the end of a 60' wire run?

I am adding an attached garage to my house. I'm going to be putting in a 100 Amp subpanel which is about 60 feet away and run through the basement joists. What gauge wire do you recommend for ...
4
votes
3answers
105k views

Where does the ground wire go in a 3-prong dryer cord configuration?

We moved to a new place where the dryer connection is 3-prong instead of 4-prong. The dryer was originally 4-prong, so we bought a 3-prong cord and installed it. It works fine, except I am not ...
13
votes
3answers
16k views

How do I run ethernet, speaker wire, and coax through a wall into a crawlspace?

I would like to run three low-voltage cables from my entertainment center through an old plaster wall, down (1-3 feet) through the sill plate, and into the crawlspace. The cables are Ethernet, ...
17
votes
4answers
47k views

Can Romex (NM-B) be run through conduit?

A few days ago I asked an electrician if I could run Romex through conduit - he gave me a funny look and said "No, Romex is not allowed in conduit." When I searched online, there seems to be a wide ...
11
votes
5answers
95k views

How should I run wiring for my above-fireplace mounted TV?

I'm going to mount my 47" LCD above my fireplace. I'm not looking for arguments against this decision. I'm looking for wiring solutions. The diagram below should help explain the situation. ...
3
votes
2answers
14k views

What is the maximum 12/2 wire length from a 20A breaker to a baseboard heater?

What is the maximum distance from a 220V/20amp circuit breaker to an 2000 watt electric baseboard heater using 12/2? At what distance would it require 10/2?
7
votes
4answers
22k views

What is the proper 'per code' method for running nonmetallic sheathed cable above a ceiling in the attic?

Can the wiring be run over the top of the ceiling joist, or must it be run through bored holes when running perpendicular to the joists? This is a non-habitable space, will have an attic entrance ...
21
votes
3answers
2k views

When doing electrical work, what do I use to check wires are safe?

If I am thinking of replacing a light switch, a light-fitting, a socket/outlet or doing other work with household wiring where there may be 120 Volts or 240 volts present ... There is already a ...
15
votes
4answers
13k views

What should I use to secure/organize data cable runs?

I am running Cat-6 and Coax in new construction. I am looking for advice/best practices on how to organize and secure the cables during the runs. I will be running 2 Cat-6 and 1 Coax to a single-...
8
votes
2answers
3k views

How do I run a wire underground to an outdoor post lamp?

I live in Geauga county Ohio. My question is three part. First what type of wire do I need to run from the house underground to a post lamp 100 feet away? Second,does it need to be in conduit and ...
7
votes
1answer
7k views

What is a split bus panel, and how do I recognize it in the field?

I'm having trouble identifying a split bus panel. I design and install Solar systems, and lately (after Mr Wiley gave a few seminars to local inspectors) the local authority having jurisdiction (AHJ) ...
5
votes
2answers
3k views

How do I wire my wall-mounted HD TV?

This image wall-mount setup should give a good idea of the current TV set up on the wall. I wanted to use a SmartStrip to power my TV and all the other devices (receiver, BluRay player, Wii, cable ...
4
votes
5answers
14k views

Can I install a Subpanel (in a seperate building) using a 3 wire connection (2 hots and 1 grounded neutral)?

Can I use a 3 wire connection (2 hots and 1 grounded neutral) to install a subpanel in a seperate structure if I install a seperate ground rod to the grounding bus in subpanel? I have 8/3 w/o ground ...
1
vote
1answer
2k views

Why isn't this 3-way wiring working?

Below is a diagram that I drew to help me rewire a couple of switches. The left switch is a standard 3-way switch. The right switch Cooper 275W-BOX combination single pole and 3-way switch. The single ...
5
votes
4answers
4k views

What are some ways to wire rear speakers in a home theater system?

I have two rear speakers, that I never use, since I don't have a good way (yet) to wire them. I have a hardwood floor. And the side of the room that is nearest to the TV+Audio source is open. So I don'...
3
votes
4answers
3k views

Is a duplex outlet's max amperage rating for each socket or the whole unit?

If you have a duplex outlet thats rated for lets say 20 amps, is the whole unit rated for 20 amps, or is each socket rated for 20 amps? Edit: So if I had a circuit that had a 40A breaker on it, could ...
16
votes
4answers
126k views

What is a GFI outlet used for, and where should I install them?

What purpose does a GFI serve? Where should they be used?
11
votes
15answers
67k views

When wiring outlets should I use pigtails or both sets of outlet screws?

I'm replacing the outlets in our house and pulled out one that had two black and two white cables. My first thought was that it was two circuits, one of them being switched, but then realized the tab ...
11
votes
3answers
49k views

How do I properly feed coax through an outside wall?

I would like to add a new cable outlet to an outside wall and wanted to find out what kind of drill bit is needed to drill through and feed the coax cable as well as anything else to be mindful of. ...
7
votes
5answers
2k views

Is it possible to convert a switched light into an unswitched outlet?

I am installing an overhead automatic garage door opener. My only power source close to where I will be hanging the motor is an overhead light socket that is operated by a switch on the wall next to ...
6
votes
6answers
21k views

Why is it safe to use 15 A receptacles on a 20 A circuit?

OK, the one answer I got was way off target, and another commenter couldn't figure out what I was asking, so I'm restating the question... Are 15A 3-prong grounded outlets actually rated to 20A, ...
1
vote
4answers
12k views

How do I wire a GFCI combination light switch when power enters at the light?

I have a Leviton 7299-NW GFCI/switch combo The diagrams in a response to the question "How do I wire a GFCI/switch combo?" is helpful. But I want to see a diagram for a situation where the power ...
7
votes
5answers
71k views

Can different gauge wiring be used in the same circuit?

I am extending a lighting and outlet circuit in a basement. The current setup has the following characteristics 15 amp. circuit breaker (200 amp service) 4 existing lighting fixtures using CFL bulbs ...
5
votes
7answers
31k views

How should I wire for a security system during construction?

I would like to run wires in anticipation of a future hard-wired security system. However, I have yet to find any information that pulls everything together regarding what is required. From what I ...
3
votes
1answer
5k views

When wiring a switch loop, which wire is which?

If you're wiring up a lighting circuit, where the power enters at the lighting outlet. According to the National Electrical Code, which wire should be "hot" and which should be "switched hot"? ...
14
votes
6answers
13k views

What is the right way to strip power wires?

I've been working with electrical circuits as a DIYer for years, including electronics and powerline work. But one thing I always feel like I do a terrible job at is stripping wires: both the outside ...
7
votes
2answers
1k views

Is a negative reading from a non-contact voltage detector sufficient?

I'm a beginner at doing electrical work, and I want to make sure I'm not taking unnecessary risks. Let's say that I'm preparing to work on some wiring. I have a non-contact voltage detector that ...
6
votes
1answer
962 views

How do I terminate coaxial cable in a crimp on F type connector?

I've got some coaxial cable, and I'd like to put F type connectors on the end so I can use the cable to connect my TV to the Cable box. How do I put ends on the cable?
4
votes
1answer
11k views

How should I wire this White-Rodgers fan and limit control? What about the thermostat?

I have a wood-burning stove, that is used as an auxiliary heat source in the house. There's a regular electric furnace, and adjacent to it is the stove. The warm air duct (out) from the stove ...
4
votes
4answers
3k views

How can I wire this three-way circuit between two buildings with only 3 conductors?

I am rewiring my entire house after a major malfunction of two antique knob and tube circuits. I'm up against a challenge with some outdoor lights. Here's the situation: I have a detached garage. It ...
4
votes
2answers
6k views

Do open-back low voltage boxes have advantages over standard outlet boxes?

I will be running LV wiring in new construction. I've seen the open backed Carlon boxes, but have read that they are difficult to insulate, and therefore should not be used on exterior walls. I ...
4
votes
2answers
1k views

Can I substitute two wires for one heavier-gauge wire?

Can I substitute two 14-gauge wires together for one 10-gauge wire? Using it from the generator RB-30 remote box, to the transfer switch inside a 6', 10-3 whip in the basement.
3
votes
2answers
1k views

Term to describe two circuits run through one /3 cable

For example, I have a 12/3 cable in which the red and black wires are controlled via separate breakers. The 12/3 drops into a single-gang outlet, out of which runs a 12/2 to another room. Is there a ...
3
votes
4answers
7k views

How can I verify that the protective earth/ground is separate from the neutral wire in an electrical AC installation?

It's easy to verify which wire is the phase without relying on wire colors. But I'm not sure if I'm able to determine which wire is the ground and which is the neutral. I have heard that using a ...
2
votes
2answers
2k views

Adding USB Dual Port Charger Receptacle Blows Mains

I purchased a Hubbell "USB Dual Port Charger with 15A Duplex Receptacle" from Lowes to replace the duplex receptacle on my kitchen island. I first opened the circuit labelled for the island. The ...
2
votes
1answer
6k views

What are the codes for electrical wiring in attics?

What is the typical code for wiring in attics? I understand these vary but what's best practice? Can you just have electrical wires exposed with all the junctions, in junction boxes, provided all the ...
2
votes
2answers
2k views

Suitability of flexible metallic conduit serving as ground

EDIT: The attached photo is the most easily accessible example of the conduit used in the entire house. This shows the conduit attached to the garbage disposal with the previously mentioned 3/4 set ...
1
vote
4answers
30k views

Adding a C wire to a new Honeywell WIfi Thermostat

I am trying to install a new Honeywell touchscreen WIFI thermostat and need to add a C wire to my terminal inside the furnace (using the help found at How can I add a "C" wire to my ...
0
votes
1answer
51 views

can I put 3 new light fixtures and switches on the same breaker

I have a person that wants to wire in four actually light boxes for ceiling fans with switches and I need to know if I can run all four of them safely from one breaker and if so what kind of breaker? ...
0
votes
1answer
52 views

How safely bring lamp wire into house?

I'm considering replacing an outdoor lighting fixture with an LED motion-sensitive fixture, but I'm not sure how to safely do the wiring. The location is protected (under a porch) but still needs to ...
0
votes
2answers
63 views

Installing grounded light fixture on box with no ground conductor

I'm installing a brand new motion activated security light to an existing box on my garage. After removing the old light, I notice it only has white/black wiring while the new light fixture has of ...
0
votes
5answers
7k views

How can I wire an exhaust fan to turn on from multiple locations?

I just bought a Panasonic FV-20NLF1 inline bath exhaust fan that I planned to used to exhaust 2 different bathrooms. I want each bathroom light switch to control the fan, so when the lighting turns ...
24
votes
6answers
38k views

How do I wire an old house with Cat6?

I have a older home (build in the 50's) with 1/2" dry wall and then plaster on top. I would like to run Cat6 cable through most of the house (living room, kitchen, entertainment room,etc). So, I'm ...
7
votes
4answers
3k views

How Do I Plan for an Intrusion Detection System?

I would like to plan for an intrusion detection system in a home that is currently under construction. The home has a walkout basement that is sloping, shown in the rear elevation picture shown below....
18
votes
3answers
13k views

Is running ethernet cable through an air return allowed under US code?

I'm looking to wire up the second floor of my house and the cold air return provides a convenient, straight run from the office to the utility room. Is it safe and within code to run ethernet cable in ...
5
votes
1answer
1k views

What should I do about old cables that have been damaged?

I was replacing some drywall and noticed the wiring underneath has a couple of surface tears. House is from the sixties, but has been rewired with new Romex, except this circuit. Wire seems to be old ...
4
votes
3answers
13k views

How to use network patch panel in new house

I just moved in to a townhouse built in 2007 with a seemingly nice CAT5 and coaxial cabling. In fact, I found a patch panel in the closet! I opened it and found this: I also noticed some ...
4
votes
2answers
17k views

Can I use SCH 40 for buried and above ground feeder wire?

I'm running 2" PVC from my house to a detached garage to run a 60 amp feeder. Looking at the NEC, it looks like I need to put it in SCH 40 below-ground. However, it looks like I have to use SCH 80 ...
11
votes
3answers
3k views

What size extension cord should I use for multiple computers?

We're hosting a LAN party (several computers, 50+) and I had some questions about power draw; I hope this is the right place to ask. Currently, we're assuming each PC will draw an average of 3.5 amps....
10
votes
3answers
11k views

Can I use two wire nuts instead of one to connect 6 wires inside a 3-gang box?

Is it considered acceptable practice to use two wirenuts in a situation where it is possible to use only one but may be easier to use two? I have a three-gang box with six cables coming into it. The ...