110 views

Sub panel and neutral and ground bus bar

Some HVAC people under previous home owners put in a sub panel box and ran the AC as well as some lighting and outlet circuits from the sub panel. The bus bars on the two sides of the panel box were ...
1
vote
0answers
55 views

Sub panel cable feed code

The inspector failed the sub panel box location because it only had 6 feet clearance and not 6.5. The electricians came and moved the sub panel box, but they did not run a new feed cable. They put a ...
2
votes
1answer
286 views

Why does a subpanel need separate ground and neutral?

Why does a power sub panel have to have separate neutral and ground bars other than code satisfaction? Does a sub panel need a main breaker if there is one at the main? Also, does the sub panel ...
1
vote
2answers
75 views

Can I replace the main breaker in an electrical panel with a smaller one?

I have an older 60amp fuse box in a rental property that is wired as a sub panel off my main 100amp service. I would like to upgrade to a new circuit breaker panel so tenants can not pull out the ...
3
votes
3answers
215 views

What is wrong with this panel wiring?

I have a main breaker panel downstairs, and a subpanel upstairs. After I hired an electrician to rerun the service entry cables, nothing upstairs is right, and all the upstairs lights blew as soon as ...
1
vote
0answers
905 views

What size wire do I need for a 100amp underground 300 ft run?

I want to put in a 100amp subpanel in my garage. The run will be underground and 300ft long. I have a Siemens panel with breakers rated at 60/75 deg C. What is the proper wire size I need? I was ...
3
votes
3answers
131 views

Why am I getting no power to the branch circuits with a new sub-panel?

My home had an ancient Zinsco sub-panel in which the breakers were grounding out and arcing to the panel. I've swapped it with a new Eaton 100 amp panel. I've re-installed all the breakers, and ...
1
vote
1answer
863 views

Can you put a small breaker panel after a 30 amp breaker from main panel in the house?

Looking to run lights in my garage. If I put a 30 amp breaker in my main panel on a 10 wire to a small breaker panel in my garage, can I put 2-4 15 amp breakers out there for the lights? Likewise, ...
0
votes
1answer
359 views

What subpanel and number of circuit breakers should I install in a detached garage?

I no longer am dealing with my contractor. Long story. But he ran 2 10-3 wires out to my garage for power. I think he was planning on putting a 30 amp breaker on the panel in the house for each wire ...
0
votes
0answers
60 views

Can I feed a 30 amp plasma cutter from this 50 amp subpanel?

The subpanel is fed from a 50 ampere 240 volt two pole breaker. Currently there are 3 20 ampere 120 volt breakers, running on it (two freezers and an air compressor). Would like to add a 30 ampere ...
1
vote
1answer
898 views

How to determine what type and gauge of wire should used for underground wiring to a detached subpanel?

I Will be installing a subpanel in a detached garage. The subpanel will be 60 amp. The garage is about 30' from the main-panel in-house, and I will of course get an exact length before selecting the ...
1
vote
3answers
326 views

How do I determine the fill rating of a conduit?

I Will be installing a subpanel in a detached garage. The subpanel will be 60 amp. The garage is about 30' from the main-panel in-house, and I will of course get an exact length before selecting the ...
0
votes
1answer
2k views

How to properly ground a subpanel in detached building?

I Will be installing a subpanel in a detached garage. The subpanel will be 60 amp. The garage is about 30' from the main-panel in-house, and I will of course get an exact length before selecting the ...
0
votes
0answers
84 views

Can two circuits feed one sub-panel while remaining separate?

I'm turning a shed into a workshop. I already have two circuits that run to nearby exterior outlets that I want to tie into to power my shed/workshop. I would like to have 1 circuit for lights and the ...
4
votes
2answers
982 views

What type of wire should I use to feed a 70 ampere subpanel?

Finishing a basement and I need to add a subpanel. Main panel is outside. Subpanel will be in the basement. 70 Amp breaker in the main to feed the subpanel. I was thinking THHN but would this mean ...
6
votes
2answers
478 views

Can an electrical subpanel go underneath plumbing?

I was about to wire up my new basement subpanel when I realized I had put it directly under a toilet. I don't think this is a code violation. I can relocate it with some difficulty. I'm also ...
0
votes
1answer
983 views

Can I connect my generator transfer switch to a subpanel instead of to the main panel?

My house has a generator transfer switch (ProTran 30310B) attached to circuits in the main panel (see photo). I added an attached garage to the house. I want to add a subpanel in the garage, ...
1
vote
1answer
842 views

Do I need conduit for an indoor sub-panel feeder line?

I'm adding a 100A sub-panel to feed a stove and water heater. The sub panel is indoors and in the same building as the mains panel. Do I need to run the supply feeder in conduit? I'm in Michigan and ...
3
votes
2answers
4k views

Can I install a Subpanel (in a seperate building) using a 3 wire connection (2 hots and 1 grounded neutral)?

Can I use a 3 wire connection (2 hots and 1 grounded neutral) to install a subpanel in a seperate structure if I install a seperate ground rod to the grounding bus in subpanel? I have 8/3 w/o ground ...
1
vote
1answer
157 views

Why is one half of a subpanel not working?

I have 12/3 wire running out to my garage. I have a double 20 amp breaker in main box and a subpanel with two single 20 amp breakers in the garage with black to one breaker and red to the other. The ...
5
votes
2answers
1k views

Does the neutral wire float or go to the neutral bus on a sub panel?

Does the neutral wire float or go to the neutral bus on a sub panel?
1
vote
1answer
205 views

Can I install a subpanel using only two ungrounded (hot) conductors and a grounding conductor?

we removed the inside part of an air conditioner / heater from a mobile home. we plan to use this area as a small pantry. The wires that were connected to the heater is 2 black connected to 2 seperate ...
5
votes
1answer
12k views

What size wire should I use to feed a subpanel in my garage?

My main panel has been upgraded to 100 amps. I would like to add a subpanel in the garage which would supply: 20 amp Mig welder running on 120 volts, but later upgrade to a larger Mig welder as i ...
0
votes
0answers
280 views

Can this wire support a 60 amp sub-panel? [closed]

An insulated single wire cable (with about 10 bundled copper wires) that is marked 900V and is about 60 feet long will carry how many Amps? I have a sub-panel in my garage that feeds from a 60 amp ...
7
votes
2answers
51k views

What wire gauge do I need for a 100 Amp subpanel at the end of a 60' wire run?

I am adding an attached garage to my house. I'm going to be putting in a 100 Amp subpanel which is about 60 feet away and run through the basement joists. What gauge wire do you recommend for ...
0
votes
1answer
160 views

Should I reorganize the main service panel when adding a subpanel?

I am currently in need of a new 240V circuit for a welder in the garage but my main breaker is full. Adding a subpanel seems to be the only solution that would be to code, but I have a couple ...
5
votes
2answers
10k views

How do I properly ground my subpanel that only has one neutral/ground bar?

I am adding a sub panel in an unattached building. My sub panel has the connection for the 2 hot wires coming from the source panel (a 40 amp double breaker) In addition it has one neutral/ground bar ...
4
votes
2answers
229 views

How can I insulate a stud bay containing a subpanel?

I'm putting a subpanel in the outside wall of my attached garage, which I'm also insulating so I can work out there in the winter. I'm wondering what steps are worthwhile to air seal and insulate ...
8
votes
1answer
1k views

What wire and conduit is required for an attached-garage subpanel?

To make my garage more usable as a workshop, I'm planning to add a subpanel which can feed a number of additional outlets. 60 amps would be plenty for my current needs, but I'd like to go with 100 so ...
2
votes
3answers
2k views

How can I install an electrical panel when the stud cavity is too narrow?

I am installing a sub panel in my garage and ran into a problem. I have the usual 14" of space in the stud cavity but the problem is that the subpanel I bought is 14 1/4" wide. I'm wondering what ...
2
votes
2answers
7k views

Can I feed a sub-panel from a sub-panel?

here is what I have. On the corner of my house, I have the main breaker box. I also have a 2nd sub panel that was installed later on the other side of the house which has 240V ac running to it. This ...
3
votes
1answer
499 views

Can I use my old service panel as a sub-panel when I install a new one?

The main panel in my building is 100 feet from the where the feed wire comes in from the outside meter. Can I install a new 200 amp panel where the feed line comes in and use the existing wire to feed ...
5
votes
2answers
5k views

How to determine the correct capacity for a sub-panel for a shop?

I plan to install a sub-panel for my woodworking shop, and would like to determine the total capacity that should supply that sub-panel. These are the main items that will likely be running in the ...
5
votes
1answer
1k views

How can I add 100 amp electrical service to a shop?

I am going to wire my shop and want ot run #2 copper to a 100amp breaker panel. I really do not have the space in the 200 amp panel in the house, my question - is there a way to pull this wire off the ...
10
votes
4answers
2k views

Would running a new subpanel in parallel meet NEC requirements? If not, what should I do?

Background U.S.A. Voltages/power present. My house has a 125A Power Mains breaker at the street. A buried line runs from the street breaker to my main panel on exterior wall outside of house. The ...