Ground fault circuit interrupter, also referred to GFCI, GFI, or a residual-current device. This devices detects a leak in current, or an imbalance between the current on the hot and neutral wires. This is used to prevent electrical shock.

learn more… | top users | synonyms

12
votes
2answers
8k views

Which Kitchen outlets do NOT need GFCI?

I have the 2 circuits in the kitchen with GFCI outlets, but I'm not quite sure which other ones do NOT need GFCI. Other circuits in the kitchen include Microwave, Fridge, and Dishwasher. It makes ...
11
votes
4answers
10k views

How do I properly wire GFCI outlets in parallel?

I have two countertop outlets in my kitchen that I am in the process of replacing with new, GFCI-protected outlets. These two outlets are on a circuit together, and they are the only loads on that ...
11
votes
2answers
4k views

When to use holes instead of side terminals to wire an outlet

This question comes from Shirlock's comment on this GFCI wiring question. When and why should you use the holes on the back of an outlet rather than the side terminals? I always assumed the holes on ...
10
votes
4answers
24k views

How do I install a GFCI receptacle with two hot wires and common neutral?

In my kitchen, I want to replace a regular 120V receptacle with a GFCI-protected receptacle. The instructions describe what to do with a regular 2-wire + ground feed, with and without daisy chaining ...
9
votes
2answers
4k views

How should I address my bathroom's flickering lights and GFCI tripping mysteriously? (Schematic included.)

So I inherited a bit of a nightmare for wiring in my bathroom. I'll be calling in an electrician, but wanted to have an understanding of the problem first, as not to be ripped off, lead astray, etc.. ...
8
votes
2answers
1k views

Is it possible to be electrocuted from a properly functioning GFCI circuit?

It's my understanding the the purpose of a GFCI circuit is to prevent shock by tripping the circuit if there is an imbalance in current in vs. current out. So my question is, if you have a functioning ...
8
votes
1answer
464 views

Can I add a standard receptacle on a GFCI circuit

So, I want to add a receptacle in the bathroom (I tend to run out of batteries on my phone while crapping at the end of the day). There's a GFCI outlet on the other side of the crapper wall that ...
8
votes
1answer
338 views

Can I have multiple GFCIs on one circuit?

I have a 70s kitchen with a very long countertop. I understand that I only need one GFCI to protect the downstream outlets (for example near the sink). However, I decided instead to install 3 separate ...
8
votes
3answers
650 views

Is an ungrounded GFCI outlet safer than a plumbing-grounded non-GFCI outlet?

I'm in the United States. I have a handful of three-prong outlets that have been grounded to the underground water main just as it enters the crawlspace. All of the ground wires are home runs to the ...
7
votes
2answers
253 views

Should switches in a kitchen area have GFCI protection?

Do the switches on the wall and over the counter areas have to be on a GFCI protected circuit? As there is live power at the switch all the time, I would think this to be true, but I'm not sure.
7
votes
1answer
325 views

Is it worth it to replace old style breakers with GFCI or AFCI breakers?

I have older wiring on my house (2-wire) BX. And while it's all in good condition, and I do check the outlets monthly to make certain it's still grounded, I'm wary of the BX sheathing as the ground. ...
6
votes
1answer
1k views

GFCI outlet won't come on

I have a couple recently installed (By a professional licensed electrician) GFCI outlets outside a barn, both on their own circuit. Both have water trough heaters plugged into them - 1500 watts each. ...
6
votes
2answers
3k views

What could be causing GFCI breakers and receptacles to trip?

I have a two wire system and after installing GFCI outlet in kitchen I realized there is a problem with some type of inconsistancy causing the GFCI to trip as soon as power is sent to it. Thinking the ...
6
votes
1answer
3k views

Why doesn't my GFI receptacle reset?

I have a GFI receptacle in my kitchen that feeds four other receptacles. It tripped the other day and I cannot get it to reset. All of the other receptables on the circuit are not functioning which ...
6
votes
4answers
2k views

What could be causing AFCI breaker and GFCI receptacle nuisance tripping?

I have a very unusual set of electrical issues that have proven difficult to troubleshoot. I live in a newly constructed house. Each bedroom has AFCI breakers. In the past 3 years living there, the ...
5
votes
3answers
553 views

Is GFCI protection required for a dedicated exhaust fan circuit?

I'm considering installing an exhaust fan in my bathroom which includes light and heat, and requires a dedicated 20 amp circuit. Would this circuit need GFCI protection? The instructions for the unit ...
5
votes
3answers
454 views

What is a UFCL brand circuit?

I'm shopping for a combination vent fan/light for a bathroom, and some of the ones I've found state this: UL Listed for use over bathtubs and showers when connected to a GFCI protected branch ...
5
votes
1answer
7k views

How do I wire a GFCI/Switch Combo?

I'm replacing an old GFCI/Switch combo. In the old one there are two wires coming into the line side, a hot wire and a neutral. On the load side there is one wire leading up to the lighting fixture. ...
5
votes
1answer
751 views

Can I connect two load lines to a GFCI receptacle?

I just bought a leviton GFCI and the instructions say if there are two load lines in the box, do not connect the GFCI in that box. I can't understand why this is a problem, especially since the ...
4
votes
1answer
1k views

Why does my GFCI outlet trip as soon as the breaker is turned on?

I have an outlet feeding other outlets about 50 feet away. All the outlets are outdoor enclosed in a protective weather cover. Today I wanted to replace one of the receptacles with a GFCI so all the ...
4
votes
2answers
246 views

Why does my circuit breaker trip with any small load, even after replacing the breaker?

I have a 20A 240V GFCI breaker in my main breaker box going to a conduit to another breaker box outside. All worked well last summer. Now, when I put any load (weed-eater, light, etc.) on an outlet ...
4
votes
2answers
409 views

GFI reset is behind refrigerator, need to remove refrigerator from circuit and relocate GFI

I am looking at purchasing a home in Florida, built in 2005. Our home inspector was not the smartest cookie in the jar, but accidently discovered some strange things. So far, this is what I have ...
4
votes
2answers
849 views

How do I replace 4 GFCI receptacles on the same circuit?

The first GFCI has not worked in years. Today a hair dryer quit, and the remaining 3 GFCIs are not working. Replaced the first one and it seemed to be working properly. Went to the last in the series; ...
4
votes
1answer
98 views

Should a GFCI interrupt the entire circuit?

I moved into a new house and never heard of this before, so I thought it was strange. On 2 circuits I've had a GFCI trip, and when they do, they trip the entire circuit. I thought they were just for ...
4
votes
1answer
6k views

How should I wire a GFCI outlet and a switch to isolate the switch but provide GFCI protection further in the series?

I am replacing the outlets for my garbage disposal/dishwasher circuit in my kitchen. Currently on that breaker there is one non-GFCI outlet with a pigtailed switch controlling the garbage disposal and ...
4
votes
1answer
69 views

Is it OK to have a GFCI downstream of a standard circuit?

I would like to extend a standard electrical circuit to the outside with a GFCI outlet. Can I install a GFCI downstream? This would be easier than running a new circuit back to the breaker panel.
3
votes
3answers
191 views

Do I need to plug my snow thrower to GFCI outlet?

I bought a snow thrower with 13.5A power. One area of my house is close to a GFCI outlet but the other side of the house is not. It's just a regular outlet. So I am not sure it can be safe to use with ...
3
votes
2answers
810 views

Do outlets in damp locations require GFCI protection?

The title says it all. It appears wet locations require not only GFCI protection but also weatherproof boxes and appropriately rated everything, but I can't find much addressing damp locations. Most ...
3
votes
4answers
547 views

GFCI not tripped, but no current downstream

I have an outside shed with a non-GFCI outlet and a light fixture. Only the light is controlled by a switch. The shed is wired off of an outside GCFI outlet. Everything, including the outlet, was ...
3
votes
2answers
1k views

GFCI buzzing on same circuit as dimmer

Ok, is please bear with a little explanation: My girlfriend had the master bath in her condo remodeled, and asked her contractor to install a new (GFCI) outlet. He apparently pulled it from the ...
3
votes
2answers
99 views

How do I wire a GFCI receptacle using two black wires and two white wires?

I recently purchased an older home and wanted to install GFCI outlets in the kitchen. When I opened up the outlet, there were four wires (two black and two white) in addition to the ground. I ...
3
votes
1answer
456 views

How can I add a GFCI breaker on two circuits with a shared neutral without rewiring? [duplicate]

Possible Duplicate: How do I install a GFCI receptacle with two hot wires and common neutral? I have a pool to protect correctly. There is a 12/3 wire: red serves the receptacles at the ...
2
votes
3answers
179 views

How can I stop this GFCI receptacle from tripping?

In my garage I have two wall receptacles on opposite sides of the garage. On one side the receptacle is a GFCI receptacle and the other side is a normal one. In the normal receptacle I have a small ...
2
votes
2answers
220 views

Why does my GFCI receptacle trip when I connect the load wires?

I was trying to install a GFCI outlet and when I install it with the five wire setup with the line on top and load on bottom, the outlet continually trips. I made sure which wire was the hot-line and ...
2
votes
1answer
145 views

What is wrong with this GFCI outlet?

I have a GFCI outlet which is testing wierdly. On one of the plugs, one prong tests hot and the other does not (using a Voltaware). On the other plug, both prongs test hot. The other outlets on the ...
2
votes
3answers
242 views

Are non-GFCI outlets that are downstream of a GFCI outlet ground fault protected if they are fed from the GFCI outlet's load side?

Are non-GFCI outlets that are downstream of a GFCI outlet ground fault protected if they are fed from the GFCI outlet's load side? If those non-GFCI downstream outlets were not fed from the GFCI ...
2
votes
3answers
58 views

How to independently switch a GFCI outlet?

I would like to add a plug outside where each plug would be independently switched. The use of this is to be able to switch a rope light and a fan separately. This is being added to a new breaker so ...
2
votes
1answer
132 views

Why is my GFCI/Switch combo working in such an odd way?

I recently moved into a new apartment, built around 1960. There was no outlet in the bathroom or within 10 feet, just a light switch. So I purchased a CFCI/Switch combo at Lowes. There were only ...
2
votes
1answer
1k views

How to add GFCI to a box with one outlet controlled by a switch?

I'm pretty inexperienced when it comes to electrical work, though I do know my way around a circuit diagram, thanks to some EE courses in college. I think this is one I can do myself, I just would ...
2
votes
1answer
218 views

Can I use a GFCI on an ungrounded 2-wire circuit at the terminus?

I mistakenly ran 18ga twin lead through plastic conduit out to power 12 volt lights. Never hooked up. Now I want to power a .68 amp 120V pump on a water feature. Too many 90 degree elbows to be able ...
2
votes
1answer
279 views

Does anyone make a gfci switch/outlet combo that includes a nightlight?

Basically what the question asked above. I've been through three stores and the closest I came was a Pass and Seymour switch/outlet combo with a snap in LED light, but it wasn't a GFCI. I'm hoping to ...
1
vote
2answers
395 views

Will an ungrounded light fixture on a GFCI circuit cause the GFCI to trip?

Shed outlet is powered from a GFCI breaker in the main panel. I want to add a switched light in the shed using power from the outlet. The outlet is a standard 20a grounded outlet, not a GFCI. No ...
1
vote
4answers
574 views

How do I wire a GFCI combination light switch when power enters at the light?

I have a Leviton 7299-NW GFCI/switch combo The diagrams in a response to the question "How do I wire a GFCI/switch combo?" is helpful. But I want to see a diagram for a situation where the power ...
1
vote
3answers
77 views

How can I remotely monitor a GFCI receptacle?

How can a sump pump in a crawl space only accessible by crawling down a hole in a closet have its GFCI protected outlet monitored from the living room? I am imagining the best way to run the pump is ...
1
vote
1answer
502 views

Why does my GFCI periodically trip, especially after a few days' rain?

I have a GFCI in my living room bath that controls a couple of lights in the basement and bedroom upstairs (weird, thats what it seems to control). Now, every 2 or 3 weeks or so, it seems to trip and ...
1
vote
1answer
82 views

Can I have GFCI receptacles on the same circuit as normal receptacles? [duplicate]

I am looking at a few books and they all show samples of circuits, but never tell or show if you can mix receptacle types. I have a circuit running to 2 bedrooms for my power outlets. The are on 12/2 ...
1
vote
1answer
593 views

Proper wiring for GFCI given switched circuit

So I've added the 3-prong plug to my garbage disposal, and now I'm on to the GFCI outlet installation. The breaker was not GFCI protected, nor is there a GFCI outlet on the loop. I've gotten to the ...
1
vote
2answers
1k views

Why GFCI clicks, even when turned off?

I have a GFCI receptacle that is clicking. Every 5-10 minutes it clicks repeatedly for 1-2 seconds. The GFCI is turned off (the RESET button is sticking out) but it still clicks! What does this mean? ...
0
votes
1answer
634 views

How do I wire this GFCI receptacle/switch combination device?

I am trying to replace a switch/receptacle combo in our bath room with a GFCI switch/receptacle combo. I am no electrician but understand wiring for the most part however this one has got me stumped. ...
0
votes
1answer
102 views

Why won't the GFCI-protected devices in my kitchen work even though they seem to have power?

I have a GFCI receptacle that will not reset, and all of the switches -- which are to my garbage disposal, dishwasher, and over-sink light -- will not work. I checked it with a voltage detector after ...

1 2